Differential Protection: CTs arrangement for star-star connected power transformes?
Engineering and workplace issues. topic
Posted by sunny on 17 August, 2008 - 9:55 am
For differential protection on a delta-star connected power T/F, CTs on delta side are connected in star & CTs on star side are connected in delta to compensate for 30 degree phase shift because of star-delta connection. What will be this arrangement for Star-Star connected T/F?


Posted by Phil Corso on 17 August, 2008 - 1:44 pm
Responding to Sunny’s 17-Aug-08 (09:55) query...

Star-Star is preferred for two reasons:

a) CT ratio's are easily determined.

b) Earthing of the CT secondary wiring is simplified.

Regards, Phil Corso (cepsicon@aol.com)


Posted by sunny on 19 August, 2008 - 12:39 am
Mr. Phil,

I didn't get it. I am asking that for a star-star connected power T/F, what would or should be CT's connection arrangement on both sides (primary/secondary) for differential protection?
Please explain!


Posted by Phil Corso, PE on 20 August, 2008 - 12:39 am
Sunny, both sets of CTs can be star-star connected, just like the T/F primary and secondary winding's are!

Phil Corso (cepicon@aol.com)


Posted by L&T on 20 August, 2008 - 12:57 am
In diff protection we have to create phase diff,
so for star star transformer cts should connected in delta delta on both sides.


Posted by Rasam Syamsudin on 31 August, 2008 - 1:28 pm
The answer is using an example of 10 kVA transformer 13.8 kV primer & 4.16 kV secondair. In CT selection 1.5 factor is implemented.
CT ratio at 13.8 kV is 75/1 and 200/1 at 4.16 kV.
CT connection is Star-Star.
CT out put for the relay is 0.836A from 13.8 kV system and 1.04 A from 4.16 kV.

This mismatch can be adjusted if we use a new relay type but for the old type we havew to select tap. Remember connect phase A to phase A, B to B, and C to C for relay relay. Ground the neutral CT at one location, recommended at relay cubicle panel.

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2009 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2009 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Internet Explorer 6.0 Fix

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!