Differential Protection: CTs arrangement for star-star connected power transformes?For differential protection on a delta-star connected power T/F, CTs on delta side are connected in star & CTs on star side are connected in delta to compensate for 30 degree phase shift because of star-delta connection. What will be this arrangement for Star-Star connected T/F?
Responding to Sunny’s 17-Aug-08 (09:55) query...
Star-Star is preferred for two reasons:
a) CT ratio's are easily determined.
b) Earthing of the CT secondary wiring is simplified.
Regards, Phil Corso (cepsicon@aol.com)
Star-Star is preferred for two reasons:
a) CT ratio's are easily determined.
b) Earthing of the CT secondary wiring is simplified.
Regards, Phil Corso (cepsicon@aol.com)
Mr. Phil,
I didn't get it. I am asking that for a star-star connected power T/F, what would or should be CT's connection arrangement on both sides (primary/secondary) for differential protection?
Please explain!
I didn't get it. I am asking that for a star-star connected power T/F, what would or should be CT's connection arrangement on both sides (primary/secondary) for differential protection?
Please explain!
Sunny, both sets of CTs can be star-star connected, just like the T/F primary and secondary winding's are!
Phil Corso (cepicon@aol.com)
Phil Corso (cepicon@aol.com)
In diff protection we have to create phase diff,
so for star star transformer cts should connected in delta delta on both sides.
so for star star transformer cts should connected in delta delta on both sides.
The answer is using an example of 10 kVA transformer 13.8 kV primer & 4.16 kV secondair. In CT selection 1.5 factor is implemented.
CT ratio at 13.8 kV is 75/1 and 200/1 at 4.16 kV.
CT connection is Star-Star.
CT out put for the relay is 0.836A from 13.8 kV system and 1.04 A from 4.16 kV.
This mismatch can be adjusted if we use a new relay type but for the old type we havew to select tap. Remember connect phase A to phase A, B to B, and C to C for relay relay. Ground the neutral CT at one location, recommended at relay cubicle panel.
CT ratio at 13.8 kV is 75/1 and 200/1 at 4.16 kV.
CT connection is Star-Star.
CT out put for the relay is 0.836A from 13.8 kV system and 1.04 A from 4.16 kV.
This mismatch can be adjusted if we use a new relay type but for the old type we havew to select tap. Remember connect phase A to phase A, B to B, and C to C for relay relay. Ground the neutral CT at one location, recommended at relay cubicle panel.
From Control Engineering magazine...
Related articles from Control
Engineering magazine- Budget-friendly temperature control unit
- Upgrading control for better polymer performance
- Software pinpoints process interactions
- BP selects SIS for UK deployment
- Here's what you need to know about controls, says Automation Federation, U.S. government
- Electrical product safety: Are testing labs needed or is a supplier's declaration enough?
- Automation vendors boost biofuels
- Cyber security issues take center stage in 2009
- AIC Series presents new high energy storage chokes
- Decrease arc flash risk with new motor control center option
Above articles copyright 2009 Reed Business Information.
Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2009 Control Technology Corporation. All rights reserved.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!