I would like some advice of how to implement remote control for chemical injection skid flow control valve from DCS.
This flow control valve has a DC motor that can turn backward and forward.
This flow control valve has a DC motor that can turn backward and forward.
It's a little hard with the information you have supplied.
If the valve has it's own motor control and a 4-20 mA signal input use a 4-20 mA signal from the DCS.
If all you have is a DC motor you can control the valve position with short Forward/Reverse pulses using 2 discrete outputs from the DCS to pick up 2 pole relays.
I presume the valve has end of travel limit switches which you would connect into the coil circuit.
You will need some sort of feedback to the DCS, either valve position or flow.
Give us the Make and Model of the valve actuator and the DCS then we can be more helpful.
Regards,
Roy
If the valve has it's own motor control and a 4-20 mA signal input use a 4-20 mA signal from the DCS.
If all you have is a DC motor you can control the valve position with short Forward/Reverse pulses using 2 discrete outputs from the DCS to pick up 2 pole relays.
I presume the valve has end of travel limit switches which you would connect into the coil circuit.
You will need some sort of feedback to the DCS, either valve position or flow.
Give us the Make and Model of the valve actuator and the DCS then we can be more helpful.
Regards,
Roy
Make and model of actuator valve is Amflo and AM7B. DCS is Honeywell.
Yes, I am thinking of control with short Forward/Reverse pulses using 2 discrete outputs from the DCS to pick up 2 pole relays. Feedback to the DCS is via flow meter.
Let me know if you have experience with AM7B as I am a little confused with the wirings.
Thanks for your help.
Yes, I am thinking of control with short Forward/Reverse pulses using 2 discrete outputs from the DCS to pick up 2 pole relays. Feedback to the DCS is via flow meter.
Let me know if you have experience with AM7B as I am a little confused with the wirings.
Thanks for your help.
The Amflow AM7B seems to be a pretty fancy mechanical valve, I couldn't find the actuator wiring on the Web.
I haven't used a Honeywell DCS but it must have the capability of generating a time duration pulse based on the magnitude and direction of error. If it doesn't have a controller with pulse outputs you can easily create some logic that uses a regular PID output, e.g.
if output > 50% pulse forward
If output < 50% pulse reverse
You can experiment with the maximum pulse length (error x factor) and cycle time.
You might want to try using a lower voltage supply to slow the motor down (smaller steps). Set a minimum dead-band so the motor doesn't get pulses that are too short to act on.
Good Luck,
Roy
I haven't used a Honeywell DCS but it must have the capability of generating a time duration pulse based on the magnitude and direction of error. If it doesn't have a controller with pulse outputs you can easily create some logic that uses a regular PID output, e.g.
if output > 50% pulse forward
If output < 50% pulse reverse
You can experiment with the maximum pulse length (error x factor) and cycle time.
You might want to try using a lower voltage supply to slow the motor down (smaller steps). Set a minimum dead-band so the motor doesn't get pulses that are too short to act on.
Good Luck,
Roy
Most DCS systems have some sort of INCREASE / DECREASE controller.
In some cases, the DCS does this with a modified version of the PID controller. In other cases it is a completely separate function.
Check your DCS documentation. If you tell us the type of control system you have then maybe someone can give you more detailed instructions on what to do.
Rob
www[.]lymac.co.nz
In some cases, the DCS does this with a modified version of the PID controller. In other cases it is a completely separate function.
Check your DCS documentation. If you tell us the type of control system you have then maybe someone can give you more detailed instructions on what to do.
Rob
www[.]lymac.co.nz
From Control Engineering magazine...
Related articles from Control
Engineering magazine- Budget-friendly temperature control unit
- Upgrading control for better polymer performance
- Software pinpoints process interactions
- BP selects SIS for UK deployment
- Here's what you need to know about controls, says Automation Federation, U.S. government
- Electrical product safety: Are testing labs needed or is a supplier's declaration enough?
- Automation vendors boost biofuels
- Cyber security issues take center stage in 2009
- AIC Series presents new high energy storage chokes
- Decrease arc flash risk with new motor control center option
Above articles copyright 2009 Reed Business Information.
Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2009 Control Technology Corporation. All rights reserved.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!