Z
I am having an issue talking to a SEL 2030
So far I have been able to talk to the SEL 2030 via the front port and gather the following info, but I am still not able to talk to it on port 14 via MODSCAN.
Below is a capture of my Comm. history with SEL.
Looking at this, could you please tell me what Device ID should I be using when I am
connecting to port 14?Port 16 is what the utility is reading from.
And should I be reading at register 40001? Should I be reading Holding register, coil status, input register?
who
COMMUNICATIONS PROCESSOR-S/N 2003216292 Date: 09/19/08 Time: 09:15:16
FID=SEL-2030-R116-V0-Z002000-D20020719 FID=SLBT-2030-R103-V0-Z000000-D20010122
Port# Device Protocol Parameters Identification
1 SEL-351S SEL 19200,8,2,N 34.5KV FEEDER 52-1
2 SEL-351S SEL 19200,8,2,N 34.5KV FEEDER 52-2
3 SEL-387 SEL 19200,8,2,N XFORMER 1 SEL 387
4 SEL-351S SEL 19200,8,2,N 69KV MAIN 152 SEL 351S
5 Unused
6 Unused
7 Master SEL 38400,8,1,N Teltone DS100
8 Master SEL 9600,8,2,N
9 Printer Ascii 9600,8,2,N
10 Unused
11 Unused
12 Other IED Ascii 19200,8,1,N SECOND WIND
13 Unused
14 Master Modbus 19200,8,2,N COMBINE HILLS 2030
15 Unused
16 Master Modbus 2400,8,2,N COMBINE HILLS 2030
F* Master SEL 2400,8,2,N
*>>sho p 14
Port communications settings for Port 14
PORT:14
DEVICE = M
PROTOCOL= M
MAP_TYPE= I
START_ID= 0
SETTLE1 = 0.0
SETTLE2 = 0.0
BUSY_DIS= N
ADDRESS1= OFF ADDRESS2= OFF ADDRESS3= OFF ADDRESS4= OFF
ADDRESS5= OFF ADDRESS6= OFF ADDRESS7= OFF ADDRESS8= OFF
ADDRESS9= OFF ADDRESS10= OFF ADDRESS11= OFF ADDRESS12= OFF
ADDRESS13= OFF ADDRESS14= 10 ADDRESS15= OFF ADDRESS16= OFF
ADDRESS17= OFF ADDRESS18= OFF
PORTID ="COMBINE HILLS 2030"
BAUD = 19200
PARITY = N
*>>sho m 14
Mathematical/move equation settings for Port 14
1 # SCADA DATA
2 000h = 01:METER
(MW)*10
3 001h = 01:METER:Q(MVAR)*10
4 003h = 01:METER:IA*10
5 004h = 01:METER:IB*10
6 005h = 01:METER:IC*10
7 006h = 01:METER:VAB(V)/100
8 007h = 01:METER:VBC(V)/100
9 008h = 01:METER:VCA(V)/100
10 009h:0;B = 1:TARGET:OUT105 # BREAKER FAILURE
11 009h:1;B = 1:TARGET:OUT107 # TRIP COIL FAILURE
12 009h:2;B = 1:TARGET:ALARM # RELAY FAILURE
13 009h:3;B = 1:TARGET:COMMT # COMM AIDED TRIP
14 009h:4;B = 1:TARGET:SOTFT # SOTF TRIP
15 009h:5;B = 1:TARGET:TLED16 # INST.50 OC TRIP
16 009h:6;B = 1:TARGET:TLED17 # TIME 51 OC TRIP
17 009h:7;B = 1:TARGET:TLED18 # FREQUENCY 81 TRIP
18 009h:8;B = 1:TARGET:TLED22 # PHASE A TRIP
19 009h:9;B = 1:TARGET:TLED23 # PHASE B TRIP
20 009h:10;B = 1:TARGET:TLED24 # PHASE C TRIP
who
5 Unused
6 Unused
10 Unused
11 Unused
13 Unused
15 Unused
*>>sho p 14
PORT:14
DEVICE = M
PROTOCOL= M
MAP_TYPE= I
START_ID= 0
SETTLE1 = 0.0
SETTLE2 = 0.0
BUSY_DIS= N
BAUD = 19200
PARITY = N
*>>sho m 14
1 # SCADA DATA
2 000h = 01:METER