I have an orifice plate installation with flanged tapping on an 8" horizontal pipe for flow measurement. The tapping, which is at 3 o'clock, is connected to a DP cell transmitter via impulse lines below the orifice.
Of late we have been having repeated blockage in the impulse line (service contains Amine, H2S, sour water and a few particulates: iron & salts, etc). This is usually at the HP side.
To ensure accurate measurement I do not envisage we move the tapping point above 3 o'clock. However, following discussion with other engineers we had a number of suggestions which I do not feel too comfortable with, hence the post to a wider audience.
Solution 1: Increase the orifice plate: the rapid drop in DP may have resulted in the buildup of particulates on the HP side. Hence a larger orifice plate would reduce flow resistance.
Solution 2: Re-orient impulse lines; with the 3 o'clock tapping, re-orient the impulse line such the DP cell is above the orifice and gravity would prevent a build up of particulates or blockages. (Wouldn't this affect the accuracy of the measurement?)
Solution 3: Use a new technology. Which one?
Ladies & gents, any contributions?
Many thanks.
Young Engineer
I have an orifice plate installation with flanged tapping on an 8" horizontal pipe for flow measurement. The tapping, which is at 3 o'clock, is connected to a DP cell transmitter via impulse lines below the orifice.
Of late we have been having repeated blockage in the impulse line (service contains Amine, H2S, sour water and a few particulates: iron & salts, etc). This is usually at the HP side.
To ensure accurate measurement I do not envisage we move the tapping point above 3 o'clock. However, following discussion with other engineers we had a number of suggestions which I do not feel too comfortable with, hence the post to a wider audience.
Solution 1: Increase the orifice plate: the rapid drop in DP may have resulted in the buildup of particulates on the HP side. Hence a larger orifice plate would reduce flow resistance.
Solution 2: Re-orient impulse lines; with the 3 o'clock tapping, re-orient the impulse line such the DP cell is above the orifice and gravity would prevent a build up of particulates or blockages. (Wouldn't this affect the accuracy of the measurement?)
Solution 3: Use a new technology. Which one?
Ladies & gents, any contributions?