Please give more details of your application so we can give you more concrete information.
Steve
MTL
www.mtlblog.com
Thank you for your reply. My understanding of IS or non IS cable is as follows, and correct me if I'm wrong.
The thing that makes a cable IS is that it is being used to carry IS circuits, with energy limitations imposed on them by some external energy limiting device such as a zener barrier or isolator. If I'm not mistaken there are no special requirements for construction of an IS cable, but I'm not sure whether any other special requirements to be complied with such as construction (ex., stranding size), conductor materials (ex., Fe, Cu, Al, T/C), parameters (ex., inductance & capacitance...
The only special requirement for cables carrying IS circuits is that they must be specifically identified as such, and they must be segregated from other non-IS circuits. The usual convention is to use blue sheathing on the cable outer, and for non IS circuits the cable generally use black sheathing on the outer. During construction these cables have to be segregated to differentiate the circuits.
An example of application is I want to connect a flow transmitter, flow control valve with positioner and turbine flowmeter at Zone 2 area. How do I determine whether it is an IS or non IS circuit for these devices, thus using a different cable to connect it plus have to install barrier at the DCS panel for the IS circuits? Your advice is very much appreciated. Thank you.
If it is to be IS, then the transmitters and positioners will need to be IS and protected by suitable barriers/interfaces mounted in the safe area. There are constraints for the cables used between the two, these mainly concern the insulation thickness and you will need to refer to the appropriate Installation standard for your country (e.g. EN60079-14 in the EU). There are restrictions on cable inductance and capacitance, but unless you have a IIC risk with long cable lengths, you will not have problems. Marking/segregation will again depend on the installation standard applying in your country.
If you want to email me offline, I will forward some of our Technical Literature.
Regards,
Steve
MTL
syates(AT)mtl-inst. com
www.mtlblog.com
- ABCs of SBCs: Single board computers for embedded control; Lego learning
- Less, more: NEMA cites less confidence; NAM sees more exports of manufactured goods
- Free webinar on Zigbee for embedded systems
- Better together? Ametek, Dresser-Rand, IntervalZero, Rexroth make acquisitions
- You need 2 monitors: This Website will prove it
- Preview: Mitsubishi iQ controls sequence, motion, process, CNC, robotics; has connectivity
- 30 new Rockwell Automation products integrate hardware, software
- Digital manufacturing: Autodesk Inventor shows component interactions
- Software certified by AT&T: Runs on PDAs, cellphones, enables mobile applications
- Research: HMI supervisory software use increases with service needs
Patronize our advertisers!