Hi,
I am new in PROFIBUS PA, and I know that it is possible to have up to 10 devices per segment in an EEx ia area. My question is, how many segments can I have in this EEx ia area? If I want to have 300 devices, and all of them in EEX ia area, that means that I can have 30 DP/PA couplers.
Another thing that is not clear is: when should I use barriers, and when segment protectors and so on? In general I understand the PA principle, but if somebody could give me real examples, I will appreciate it.
Thanks in advance.
Benjamin
I am new in PROFIBUS PA, and I know that it is possible to have up to 10 devices per segment in an EEx ia area. My question is, how many segments can I have in this EEx ia area? If I want to have 300 devices, and all of them in EEX ia area, that means that I can have 30 DP/PA couplers.
Another thing that is not clear is: when should I use barriers, and when segment protectors and so on? In general I understand the PA principle, but if somebody could give me real examples, I will appreciate it.
Thanks in advance.
Benjamin
I will recommend the following PROFIBUS in process brochure pages 12 and 18:
https://www.automation.siemens.com/infocenter/order_form.as px?Lang=en&tab=3&nodeKey=key_517576&docID=582
Call me if you need further assistance.
Regards
Moin
Cell: 215-9174989
https://www.automation.siemens.com/infocenter/order_form.as px?Lang=en&tab=3&nodeKey=key_517576&docID=582
Call me if you need further assistance.
Regards
Moin
Cell: 215-9174989
Thanks it was very helpful.
I also found this formula on the Siemens hompage:
https://support.automation.siemens.com/WW/llisapi.dll/2156 2130?func=ll&objId=29421329&objAction=csView&ClusterID=294209 74&nodeid0=23654018〈=en&siteid=cseus&aktprim=0& extranet=standard&viewreg=WW&load=treecontent&subtype=133000< br>
You can use the following formula for the theoretical maximum number of PA slaves per PROFIBUS master system (max. 125 DP slaves per master system):
* Ex version (hazardous area) of the DP/PA link (6ES7 157-0AD82-0XA0):
Number = 125 DP/PA links * 5 DP/PA couplers * 10 PA slaves (per DP/PA coupler) = 6250 PA slaves.
* Non-Ex version of the DP/PA link (6ES7 157-0AD82-0XA0):
Number = 125 DP/PA links * 64 PA slaves per IM157 = 8000 PA slaves.
Regards,
benjas
I also found this formula on the Siemens hompage:
https://support.automation.siemens.com/WW/llisapi.dll/2156 2130?func=ll&objId=29421329&objAction=csView&ClusterID=294209 74&nodeid0=23654018〈=en&siteid=cseus&aktprim=0& extranet=standard&viewreg=WW&load=treecontent&subtype=133000< br>
You can use the following formula for the theoretical maximum number of PA slaves per PROFIBUS master system (max. 125 DP slaves per master system):
* Ex version (hazardous area) of the DP/PA link (6ES7 157-0AD82-0XA0):
Number = 125 DP/PA links * 5 DP/PA couplers * 10 PA slaves (per DP/PA coupler) = 6250 PA slaves.
* Non-Ex version of the DP/PA link (6ES7 157-0AD82-0XA0):
Number = 125 DP/PA links * 64 PA slaves per IM157 = 8000 PA slaves.
Regards,
benjas
From Control Engineering magazine...
Related articles from Control
Engineering magazine- Smart vision sensor features simple setup, high-speed inspection
- Youth: Name a Mars rover; get your hands on Science Chicago
- Cameras with DSP coprocessors offer multiple options
- GHS has EAL6+ operating system security certification; launches Integrity Global Security
- High-speed vision system with multi-camera platform
- Synapse Wireless California Eastern Laboratories form partnership
- Automation acquisitions, expansions: Are you next?
- Open-standard nanoETXexpress Computer-on-Modules form factor gets more support
- Motors, drives and motion control: Green Hills Software tapped for Saab UAV
- Motors, drives and motion control: Moving ahead at Solar Power International trade show
Above articles copyright 2008 Reed Business Information.
Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!