Profibus PA segments allowable in EEx ia
Application Questions and Problems topic
Posted by benjas on 10 October, 2008 - 2:01 am
Hi,

I am new in PROFIBUS PA, and I know that it is possible to have up to 10 devices per segment in an EEx ia area. My question is, how many segments can I have in this EEx ia area? If I want to have 300 devices, and all of them in EEX ia area, that means that I can have 30 DP/PA couplers.

Another thing that is not clear is: when should I use barriers, and when segment protectors and so on? In general I understand the PA principle, but if somebody could give me real examples, I will appreciate it.

Thanks in advance.

Benjamin


Posted by Moin Shaikh on 10 October, 2008 - 3:26 pm
I will recommend the following PROFIBUS in process brochure pages 12 and 18:

https://www.automation.siemens.com/infocenter/order_form.as px?Lang=en&tab=3&nodeKey=key_517576&docID=582

Call me if you need further assistance.

Regards

Moin
Cell: 215-9174989


Posted by benjas on 14 October, 2008 - 3:05 am
Thanks it was very helpful.

I also found this formula on the Siemens hompage:
https://support.automation.siemens.com/WW/llisapi.dll/2156 2130?func=ll&objId=29421329&objAction=csView&ClusterID=294209 74&nodeid0=23654018&#9001;=en&siteid=cseus&aktprim=0& extranet=standard&viewreg=WW&load=treecontent&subtype=133000< br>
You can use the following formula for the theoretical maximum number of PA slaves per PROFIBUS master system (max. 125 DP slaves per master system):

* Ex version (hazardous area) of the DP/PA link (6ES7 157-0AD82-0XA0):
Number = 125 DP/PA links * 5 DP/PA couplers * 10 PA slaves (per DP/PA coupler) = 6250 PA slaves.
* Non-Ex version of the DP/PA link (6ES7 157-0AD82-0XA0):
Number = 125 DP/PA links * 64 PA slaves per IM157 = 8000 PA slaves.

Regards,
benjas

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Internet Explorer 6.0 Fix

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!