Connect to PLCs

A

Thread Starter

a_m_shiha

If we need to connect an instrument to a PLC, what is the maximum cable distance that I can use as a rule of thumb? For example pressure switch (DI).
 
V

Vinod Kumar KG

Be more specific when you ask questions to get precise answers.

If you are hard-wiring, the total length depends of the type of cable and its ohms/meter and the PLC input voltage rating, etc. If you are connecting over a network, again the distance varies depending on the media and the protocol.
 
If the pressure switch has a dry contact relay that is switching 110 vac back to the PLC for a DI, you can most likely go the length of your facility. A 110 vac input card typically looks for 85-130 vac as a high which allows for very long lengths despite voltage drop. If the pressure switch is providing or switching a 24 vdc signal you could find yourself limited to as little as a 50 foot run depending on wire size and power supply size. Hope that helps.
 
R
"switching a 24 vdc signal you could find yourself limited to as little as a 50"

Sorry, I have to disagree with that. 24 VDC will be better for extreme distance. The input modules are high impedance. On the other hand 120 VAC is limited by the inter-conductor capacitance which will cause input to remain on if it is too high (cable too long). A few hundred feet is OK.

If you have solenoids sharing the same cable it's important to use a reversed biased diode (for DC) or MOV (for AC) across the coil otherwise the inductive spike on Turn-off is enough to trigger an input.

Roy
 