Jump to a Date
Twitter Feed
Thermal Overload
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
- PC reliability?
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Why pay?
H. L. Mencken suffers from the hallucination that he is H. L.
Mencken -- there is no cure for a disease of that magnitude.
-- Maxwell Bodenheim
www.control.com/rss/
When should I use a MCB and when a glass fuse for a control system?
What is the application? A specific I/O point? Circuit breakers get real expensive if you want to put one on every I/O point.
The application is for a control system with a PLC, Analog & digital IO cards. Input voltage from ups is 110VAC. Supply to solenoids (DO) is 24VDC. Please suggest where I should use an MCB and where a glass fuse and why. Thanks.
I like to use MCBs for anything that is common to a group of circuits, e.g. power supplies, modems, PLC racks, etc. There is nothing worse than blowing a fuse and not having a spare on hand. A breaker can be quickly reset.
Fuses are OK for individual loops.
Note: Avoid the indicating type on 4-20 mA loops, if you blow a fuse the LED indicator will allow about 16 mA then max out, allowing you to think the loop is still OK but could cause tank overflow, etc.
Roy
Roy