I read and write to address areas in the PLC of V2000 - V4777. Everything seems to work fine but the application sends a zero to register V2446 to clear it and it will not write anything to it. The value stays the same unless I edit that value in the PLC program. Nothing is overwriting it.
I am using the new H0-ECOM100 with Modbus TCP/IP and have not put any special configuration in it other than the IP and Subnet Mask.
Works fine just won't write to some of the registers.
Then again, you would not be able to change V2446 with your programming software, and have the value persist, if the Modbus/TCP master were actually writing 0 to it.
My guess is that you have not correctly converted the octal DL06 addresses to decimal Modbus addresses.
If you're suspicious of the Modbus/TCP master you are using, I suggest you download one or more of the free (or shareware) Modbus/TCP masters available.
- ABCs of SBCs: Single board computers for embedded control; Lego learning
- Less, more: NEMA cites less confidence; NAM sees more exports of manufactured goods
- Free webinar on Zigbee for embedded systems
- Better together? Ametek, Dresser-Rand, IntervalZero, Rexroth make acquisitions
- You need 2 monitors: This Website will prove it
- Preview: Mitsubishi iQ controls sequence, motion, process, CNC, robotics; has connectivity
- 30 new Rockwell Automation products integrate hardware, software
- Software certified by AT&T: Runs on PDAs, cellphones, enables mobile applications
- Research: HMI supervisory software use increases with service needs
- Process modeling: Spreadsheets support multiphase flow simulation
Patronize our advertisers!