I have a new problem this week. The liquid fuel stop solenoid 20FD-1 did not open when the logic L20FD1X is forced to ONE. This is done on weekly basis to prime up the liquid fuel line.
With the solenoid not connected, I could get the 125Vdc supply when the logic is forced but once I connect the solenoid and measure the voltage in parallel, I could get only 24Vdc when the logic is forced. I have tried to replace the solenoid with a new and the result is still the same. I did try on the other unit which works well (so far
) and the solenoid operates without any problem.
The solenoid is connected on SO17 on the DTBC on <QD1) core. The DTBC module is relatively new (was replaced recently due to short circuit of 20PG2-X and all the jumper setting (M17 and P17) are in place correctly.
There were no current flow to the solenoid as well when it is forced. The valve was able to be operated smoothly by hand. Any one has any idea on what may gone wrong? Your advice is highly appreciated.
With the solenoid not connected, I could get the 125Vdc supply when the logic is forced but once I connect the solenoid and measure the voltage in parallel, I could get only 24Vdc when the logic is forced. I have tried to replace the solenoid with a new and the result is still the same. I did try on the other unit which works well (so far