Posted by JM on 12 March, 2009 - 9:10 am
What is/are the limitation of the GE PFR? Presently, our GT baseload is around 235 MW with these kind of ambient temp and humidity. Example my GT at 200 MW PSL and a big power station tripped which cause the grid frequency to fall from 50 hz to 48 hz (just to exaggerate things), does my GT will pickup up to baseload only (temp control) am I right? TTRXB/TTRX are 656.6oC and 648.9oC respectively for maximum limit (Isothermal). TTRXB/TTRX is 610oC during baseload.

Why there is no more Peak load selector in our plant? In my previous experience in a 32 MW GE gas turbine Mark IV, we have PSL, Baseload and Peak load selector. During baseload, exhaust temp was 560oC and if I remembered it right at peak load, exhaust temp setpoint was 580oC. (12 years ago).

Another situation, If my GT is at 70 MW PSL, and suddenly too many feeders tripped (again let's exaggerate things), grid frequency will increase too much. Does my GT will trip on reverse power cause it will try to regulate the frequency? Or it will limit only to minimun load of 25 MW? 25 MW is the minimum load (Spinning reserve as per GE definition) during start up. I can see in RUN status: Spin_Res.

What is the meaning of Secondary Frequency Response (Regulation)? Does all GE gas turbine have this kind of control?

Thanks.


Posted by CSA on 14 March, 2009 - 1:25 am
Primary Frequency Regulation just says that if you are operating the unit on Pre-Selected Load Control with Primary Frequency Response enabled that the unit will respond to frequency excursions by adjusting load in response to the frequency change in order to try to help maintain grid frequency. And, as always the unit can never load past CPR-biased exhaust temperature control limit, whether it's responding to frequency excursions or operator commands.

Peak Load (and Peak Reserve Load) is(are) a purchased option(s) for most machines; you want it, you got to pay for it. Many, but not all, F-class units are not capable of Peak Load; they are already running at the limit of the capability and materials of the machine.

If your unit is operating at Part Load (NOT Pre-Selected Load Control) and the frequency tries to increase, the Speedtronic will decrease the output to try to maintain frequency. But, if it's not the Isochronous machine, it won't control the frequency very well without some manual operator intervention, especially if it's the largest unit remaining on the grid.

If your unit is operating on Pre-Selected Load Control and Primary Frequency Response is *not* enabled, then the output will remain at 70 MW because the operating reference is a load setpoint and even if the frequency changes the Speedtronic will adjust the output to maintain 70 MW, so it will make the situation worse.

If your unit is operating on Pre-Selected Load Control and Primary Frequency Response *is* enabled, then the output will change as the frequency changes to try to maintain a stable frequency. BUT, if it's not the Isochronous unit and it is the largest generator remaining on the grid, then it won't do a very good job of frequency control without some manual operator intervention.

If the load decreases sufficiently to drive the unit to negative real power, the generator breaker will open on Reverse Power. Reverse Power is not generally a turbine trip, just a breaker-opening event. But, it really depends on the stability of the grid, how big the other units on the grid at the time are and if any of the other units are in Isochronous control. If the grid is down to one generator and it's operating in Droop speed control, it's not going to control frequency very well without some manual operator intervention or unless it is switched to Isochronous Speed Control.

Spinning Reserve is usually an adjustable setpoint, and it is usually only displayed immediately after a successful automatic synchronization during a unit start sequence. Unless the unit has some very unique sequencing or unique displays or a display problem, the only time Spinning Reserve will be displayed is after a successful automatic synchronization during a unit start-up.

Secondary Frequency Regulation, as generally interpreted, means some kind of "remote" frequency control being used to adjust a generator's output to control grid frequency. That's usually done with a hardwired analog (4-20 mA) signal or RAISE/LOWER contacts to drive the turbine speed reference, and usually some regulatory body or supervisory agency uses one of these methods to control a unit's output remotely.

No; most GE machines don't have this. It's usually a purchased option, and it's usually called External Load Control or Remote Load Control or AGC (Automatic Governor Control) Control.


Posted by JM on 15 March, 2009 - 5:11 am
Thanks CSA.

So, if my GT is operating on 70 MW PSL and frequency really goes high, it will trip on reverse power. There will be no minimum load (or deadband) in operating the unit.

I am thinking that it will just hold to minimum load (lower load limit) of the GT which is 25 MW load and if the frequency really goes high, GT 52G will trip by overfrequency 81O (G60 = 51.5 Hz, ABB REG 316 = pickup1 51.5 Hz and pickup2 52 Hz)as per tripping matrix and unit will stay on FSNL.

If the frequency goes low, the upper limit is CPR biased exhuast temperature limit or they called load limiter to the other control system. Just like in Base load operation, even PFR is ON, GT will not response anymore and in reality it will reduced the actual load due to reduction in speed which cause reduction of airflow, Am I right?

After annual Combustion Inspection outage, I&C will do tuning, so this PFR will always selected to OFF during tuning to prevent any load variation during frequency disturbance (deviation).

What is the difference between REVERSE POWER during frequency high and REVERSE POWER during normal shutdown? During normal shutdown, 52G will open approx 5 MW. You told (CSA) that 52G will open on reverse power during negative real power.

Can anyone explain to me how to calculate the exact MW load the generator 52G will trip during reverse power. The following data as follows: G60 reverse power (32) PT ratio: 1570/110, CT ratio 15000/1, settings stage 1 min 0.043 pu, delay 10 s (blocks while LCI in service). ABB REG316 (32) PT ratio: 1570/110, CT ratio 15000/1, P settings: -0.07, angle 30, drop ratio 60, delay 10s, PN 0.8.

So, secondary frequency regulation is AGC or Remote Load Control. We have this kind of regulation, it is control by our Toshiba DCS. We already tested this AGC, the Load Dispatch Center will give the load command for our GT GE 9FA Mark VI with some limitation. This AGC only operates during testing (commissioning) and never use again. We still do the basic load change by calling on the phone by the Load Dispatch Center.

Thanks.


Posted by CSA on 16 March, 2009 - 12:49 am
Many Speedtronic turbine control panels will trip the generator breaker on reverse power before the 32 relay; the 32 relay is used as a back-up to the Mark V or Mark VI. *In general* and unless otherwise directed or requested, the Speedtronic is programmed to open the breaker on negative MW, but on occasion some sites require or request to set the "reverse power" trip to a slight positive value, might even be 5 MW. You should look at your sequencing/application code to be sure.

I have never heard of a "lower load limit", but that doesn't mean one can't be programmed into the unit. You should look at your sequencing/application code to be sure.

The exact, precise details of how your unit operates are detailed in the sequencing or application code which is running in the Speedtronic of your unit. No written description or forum answer can over-ride what's programmed into the Speedtronic panel. I was providing general information; apparently your site is different. You should look at your sequencing/application code to be sure.

If you have some tripping matrix which outlines how your unit operates, then you should have the answer to your questions.

PFR will only adjust load when the unit was operating at a Pre-Selected Load less than Base Load. If it increases power output to CPR-biased exhaust temperature control (Base Load) because of a decrease in frequency, then the reduced power airflow will cause a reduction in power at Base Load.


Posted by JM on 16 March, 2009 - 6:55 pm
Thanks CSA, I just checked the Mark VI manual today and it states that:

REVERSE POWER SEQUENCING

The generator breaker is tripped on reverse power sensing, in the standard shutdown sequence. Reverse power rather than drop out of 4's alone is necessary because of the risk of coincidental fuel system malfunction that could cause ovespeed. Breaker opening is allowed only with 4 trip or shutdown 94x. The breaker is not allowed to open with other possible control malfunctions which could lead to overspeed.

Time delay on the reverse power relay is provided to allow for load transients while synchronizing. Turbine trips cause motoring of the generator for the time delay on reverse power sensing.

On new units, a megawatt setting is compared with the DWATT signal in place of the reverse power relay. This allows smooth shutdown with minimun draw on system megawatts.

Now, it is clear to me that during shutdown sequence, there is a MW setting to open the 52G which is 5 MW load. Before, my understanding the 32 relay is giving the command to open the 52G.

Today, we are on the process in testing the AGC control. All load changes was done by LDC (Load Dispatch Center). GT load High/Low Limit are available. High limit (224.2 MW) was based on the actual ambient and humidity while Low limit (140 MW) was selected to prevent from removing from premix mode.

I trend the system frequency during our GT#2 tripping, frequency fell from 50 Hz to 49.87 Hz. GT#3 pick up from 200 MW to 210 MW only. GT#1 on annual outage. At 4% droop setting, GT#3 should pick up around 15.275 MW (based on 235 MW full load calculation) but it pick up 10 MW only. LDC asked me why GT#3 only pick up 10 MW? Frequency still not reached 50 Hz. Is there any deadband/limit in Mark VI to prevent to increase to CPR-biased exhaust temperature control limit? I hope somebody can answer this question.

Before, I also work in 647 MW Coal Fired Thermal Plant with Alspa P320 DCS control but later it migrates to Emerson Ovation. During Alspa P320, Frequency compensation is applied in the load control loop, when there is a change in grid frequency the Auto Load control set point is adjusted by application of the frequency compensation term KDeltaF MW (up to a maximum of 50 MW) with a droop setting of 5%. The Upper Level Load Controls and the Base Level Regulator both support the free governing action.

For very large frequency fluctuations, if the Upper Level Load Control logic detects a large error (>=100 MW) in the Auto Load Control(ALC) loop, it will switch from Auto Load Control into Direct Load Control(DLC). The actual MW on the Unit will depend on the actual Load set point at the time of engaging Direct Load Control, and the application of KdeltaF in the Base Level Regulator.

I given this information (maximum of 50 MW load frequency compensation in Alspa P320), just in case there is a similar limitation from Mark VI to increase to a certain load and prevent to reach the CPR-biased exhaust temperature control limit. I also thinking that there might be a deadband/limit in reducing the GT load during high frequency.







Posted by CSA on 17 March, 2009 - 11:20 am
Any information you find in a GE manual is generic and should be considered as a guide for how the Speedtronic might be programmed. Consult your application code in the .m6b file running in the Mark VI at your site for the exact details of how the Mark VI is programmed and will operate at your site.

We don't have any details about how the units were connected to the grid, what other units were operating at the time; nothing. For Droop speed control to increase or decrease load it is necessary for there to be a difference in frequency, and we don't know what load, if any, other units might have picked up during this testing. Many times, these "tests" are deemed to be failures because they are improperly conceived and executed. If there were other turbines operating at the time in parallel with your units, and they were being operated in Droop mode, then it's likely they picked up some load as well.

We can't comment on how any other control system was programmed in relation to how the Speedtronic control system was programmed. Please consult the OES for these units for any details and assistance with the results of your testing. Please don't assume that every turbine control system will respond similarly to load or frequency disturbances. Please take all factors of operation into account when making any decisions about the success or failure of any testing. Please remember: Droop speed control is straight proportional control.


Posted by venu on 28 March, 2009 - 4:18 pm
When the GT is in PSL when frequency raises GT will start unloading if and only if the rate of raise of frequency is more than the TNKR1_4 value which is 0.33%/min. In the above condition your speed error signal will become negative, which will reduce FSRN inturn your load will come down so if the frequency raise is more 52G may open on reverse(not on low forward power). This can be prevented either by raising TNKR1_4 value or by reducing FSKNG value.

In the same way when frequency drops load on your machine will increase but restricted by TTRXB.

regards
venu

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Ducharme's Axiom:
If you view your problem closely enough you will recognize
yourself as part of the problem.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive