Control.com community I am looking for clarification on mechanical vs electrical overspeed on our MKVI controlled Frame 7EA commissioned in 2005. I understand in the days past of Frame machines that there was an overspeed bolt on the accessory gear to trip the unit on mechanical overspeed (we have an older Frame 5 that uses this), and then overspeed logic in the protection core assembly to trip the unit on electrical overspeed.
On our Cimplicity screen there is a choice to select a mechanical overspeed test or an electrical overspeed test. Since we have no overspeed bolt I have been reviewing logic to find out what the mechanical overspeed selection does. In our MKVI application code if either electrical or mechanical overspeed test is selected, a select block sends the control constant (TNKHOS) of 110% to the L12HV1 overspeed detection algorithm in MKVI application code. If the mechanical overspeed test is selected a signal L83HOST_P will also go true which feeds to the protection core as input OfflineOS1test. From what I read in our case this raises the original OS_Setpoint_PR1 in (P) core from 3960 rpm to 4086 rpm via a configured signal space input OS_Tst_Delta with a value of 126, in essence raising the OS trip setpoint for the protection (P core) from 110% to 113.5%. But since we have no overspeed bolt to trip the unit this does nothing but raises the trip setpoint, and because the MKVI application code overspeed trip setpoint is still 110% the application code in the MKVI will still trip the unit at 110%.
So is this just some leftover logic and graphics from GE? Is this a way to test MKVI application code trip logic independent of (P) core trip logic? Or am I over-analyzing this as usual!! Thanks to all for your thoughts, I have been reviewing GEH-6421G volume #1 applications for the VPRO Protection logic-overspeed trip,HP for my studies into this.
On our Cimplicity screen there is a choice to select a mechanical overspeed test or an electrical overspeed test. Since we have no overspeed bolt I have been reviewing logic to find out what the mechanical overspeed selection does. In our MKVI application code if either electrical or mechanical overspeed test is selected, a select block sends the control constant (TNKHOS) of 110% to the L12HV1 overspeed detection algorithm in MKVI application code. If the mechanical overspeed test is selected a signal L83HOST_P will also go true which feeds to the protection core as input OfflineOS1test. From what I read in our case this raises the original OS_Setpoint_PR1 in (P) core from 3960 rpm to 4086 rpm via a configured signal space input OS_Tst_Delta with a value of 126, in essence raising the OS trip setpoint for the protection (P core) from 110% to 113.5%. But since we have no overspeed bolt to trip the unit this does nothing but raises the trip setpoint, and because the MKVI application code overspeed trip setpoint is still 110% the application code in the MKVI will still trip the unit at 110%.
So is this just some leftover logic and graphics from GE? Is this a way to test MKVI application code trip logic independent of (P) core trip logic? Or am I over-analyzing this as usual!! Thanks to all for your thoughts, I have been reviewing GEH-6421G volume #1 applications for the VPRO Protection logic-overspeed trip,HP for my studies into this.