ring type metering CT wound on the primary 132 kV cable was found defective after high voltage test
consequences :
ring type metering CT was commisioned along with protection cores and found good.
152 kV high voltage test was carried out in the cable. CTs were short cktd and earthed during the test. 152kV was applied in all 3 phases together for 60 minutes. After high voltage test was completed Protection cores was found good. But metering CT shows resistance in Megaohms. but the magnetization characteristic and Knee point voltage as normal.
what will be the cause for the problem; class of metering CT is 0.5FS5
consequences :
ring type metering CT was commisioned along with protection cores and found good.
152 kV high voltage test was carried out in the cable. CTs were short cktd and earthed during the test. 152kV was applied in all 3 phases together for 60 minutes. After high voltage test was completed Protection cores was found good. But metering CT shows resistance in Megaohms. but the magnetization characteristic and Knee point voltage as normal.
what will be the cause for the problem; class of metering CT is 0.5FS5