I have an EExe certified enclosure (a junction box). Can I stick two MCB's and few fused terminals in it without sacrificing the certification. In case a fuse blows, it happens within its sealed glass tube. In case an MCB drops on account of overload, the switching will take place within the MCB housing.
Regards
VK Aggarwal
Regards
VK Aggarwal
No - one of the conditions of use for an Exe box is that it cannot contain any potentially sparking components (unless these are protected using another method - you can have for instance an Exd protected switch in an Exe enclosure).
A fuse may have an external temperature that is elevated even at rated current.
A fuse may have an external temperature that is elevated even at rated current.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.