from the Instrument & Control department...
Measuring Low Flow than Actual
Sensor technologies. topic
Posted by Qasim Maqbool on 19 August, 2009 - 7:06 pm
I am Facing Low Flow measuring Problem in Electromagnetic Flowmeter Siemens SITRANS F M MAGFLO Model MAG 6000.
I Tried all Troubleshooting Problem as mentioned in its vendor Manual.
I have also try to change it excitation frequency but unable to get result. I also switched off its Power supply for 15 minutes and again ON. But it is still in his own MOde, Showing low measuring Value.
Kindly give me Suggetion.
qasim_maqbool@live.com
Posted by Jason Semple on 16 September, 2009 - 7:34 am
How old is the meter and where are you located? Siemens have a Field Checklist which steps you through the field checks to help diagnose any potential problems with the flow meter.
I could email you the checklist if you like.
Jason
Posted by Ross on 16 September, 2009 - 10:26 am
A few particulars to check:
- Check that the units of measure are set correctly.
- Confirm that the pipe is full.
- Compare the displayed flow with actual. Is it off by a constant factor?
- Look at both flow rate and total - are both off?
Posted by Roy Matson on 16 September, 2009 - 2:03 pm
One problem I have seen in mag flow meter was one of the elsctrode seals leaking causing a low resistance to ground. This effectively cuts the voltage in half with a corresponding drop in signal output.
Just empty the tube, disconnect electrodes and check resistance.
Roy
Posted by Dave Scarlett on 25 November, 2009 - 7:38 pm
Siemens has a "Varificator" that can fully check the condition of their flow meter on line. I suggest you contact your local rep.
Too much of everything is just enough.
-- Bob Wier