AB PLC5 CH 0 to AB Power Monitor 3000
Communications systems and equipment. topic
Posted by ScratchShooter on 16 September, 2009 - 10:37 am
I am trying to use the PLC5 MSG command to pass power monitoring information from an Allen Bradley Power Monitor 3000. Since the native port for the PowerMonitor is RS485, I have to use an RS485 to RS232 coonverter..AB Eng OOPS! Has anyone had to work this little fiasco out?


Posted by Ken Roach on 16 September, 2009 - 9:12 pm
I don't see any problem with the system you describe.

I would by instinct use a 1761-NET-AIC RS-232/485 signal converter, but the PLC-5 serial port should be selectable for RS-485 signaling itself. I would be more comfortable with the NET-AIC.

The PLC-5 Channel 0 serial port is configurable for DF1 Half Duplex Master mode, and the PowerMonitor 3000 serial port is hard-set for DF1 Half Duplex Slave.

The PowerMonitor emulates PLC/SLC data tables, which are well documented in the PowerMonitor user manual.

Do you have a specific problem that you need help with, or are you more generally asking if the two devices can communicate ?


Posted by ScratchShooter on 22 September, 2009 - 1:19 pm
Thanks for the reply Ken. I don't usually use this forum for support and most of the time I get good support from Rockwell, but in this case I have the finger pointing and very few details.

My PLC5 Ch 0 does RS232, RS423, and RS422A. Not RS485. I do have an Aten IC-485S RS232 to RS485 converter to do the protocol conversion.

The Power Monitor instruction manual Pub 1404-IN007D-EN-P has no PLC5 MSG ladder examples or samples of ASCII strings. Details would be helpful if anyone has them.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
A journey of a thousand miles begins with a cash advance.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive