Hi
Please help me
I am using HP compaq Laptop. Unfortunately due to Earth fault occurred in my company, my 9-pin serial port was not communicating/working properly.
I was using this Laptop for Allen Bradley PLC programming.
Ok now I use 1747-uic converter (DH 485 to USB) to communicate my PLC with laptop. This is possible when my processor is configured in DH485 in channel -0 under drivers.
No i want to communicate my my laptop using DF1 full duplex configured in channel-o of SLC processor to my USB adapter.
For this can i Use 9300-USBS.Is that true??
Please help me
I am using HP compaq Laptop. Unfortunately due to Earth fault occurred in my company, my 9-pin serial port was not communicating/working properly.
I was using this Laptop for Allen Bradley PLC programming.
Ok now I use 1747-uic converter (DH 485 to USB) to communicate my PLC with laptop. This is possible when my processor is configured in DH485 in channel -0 under drivers.
No i want to communicate my my laptop using DF1 full duplex configured in channel-o of SLC processor to my USB adapter.
For this can i Use 9300-USBS.Is that true??
Yes, the 9300-USBS is fully supported for DF1 Full Duplex communications to all Allen-Bradley controllers and devices.
Another device I like a lot is the Keyspan USA-19HS. It will work with every A-B device I have tried except with the serial port of the 1761-NET-ENI converter module.
Another device I like a lot is the Keyspan USA-19HS. It will work with every A-B device I have tried except with the serial port of the 1761-NET-ENI converter module.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.