Delay in a VFD ?

L

Thread Starter

lalas

I am analyzing a tank (open from top with continuous feed). The level is controlled by the motor (via the VFD). When the VFD is increased from 30% to 50%, it is taking 3 minutes to see the level start going down in the tank. could that be because the VFD settings have been configured to have a 3 minute delay? I believe it is a process delay since it is a huge tank. I would appreciate any feedback.

Thanks
 
C

curt wuollet

Why don't you configure the VFD to show frequency and see if it is responding or if ramps are configured, etc.

Regards
cww
 
A
I've seen engineers spending hours trying to tune the level control in a big tank. Presume you are measuring the level, comparing it in a controller that sends a speed set point to the Vsd. Try a high gain between 5 and 7 with very little integral action. You will be surprised.

Alternatively you may be using the settings in the VSD. Any reason why you cannot go above 50%?

Lets have your settings please.
 
one way to find out is if u have an analogue input signal coming from the VSD, see if this increases when u increase from 30 to 50% output. If if does then it is a process delay.
 