So right now we have a couple 90-30s running Control for the ladder logic and they also have the open process for all the function block logic... I am not too familiar with open process. As far as I know there are utilizing the start stop auto manual blocks in Cimplicity that ties directly to a function block in open process.
So my question i guess is... Is there a way to Tune a PID_ISA block from Cimplicity? I know with the MKVI or an innovation series controller you call specify the black and the point I.E. 3100:IN2
Is there something similar to this in proficy?
Side note: Oddly enough the function blocks there using in open process are Allen Bradley STRTSTOP -Digital Hand/Auto faceplate blocks....
I have never seen this done before for GE controllers.
So my question i guess is... Is there a way to Tune a PID_ISA block from Cimplicity? I know with the MKVI or an innovation series controller you call specify the black and the point I.E. 3100:IN2
Is there something similar to this in proficy?
Side note: Oddly enough the function blocks there using in open process are Allen Bradley STRTSTOP -Digital Hand/Auto faceplate blocks....
I have never seen this done before for GE controllers.
Yes, you can access the registers of the PID_ISA from CIMPLICITY to tune the block. You'll need to create tags in CIMPLICITY that point to the registers in the PID's 40-word data block where the P, I, and D gains are located.
If you want to discuss further, please contact me off-list.
Drake Fink
Sr. Application Engineer
GE Fanuc Intelligent Platforms
drake.fink [at] ge.com
If you want to discuss further, please contact me off-list.
Drake Fink
Sr. Application Engineer
GE Fanuc Intelligent Platforms
drake.fink [at] ge.com
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2009 Nerds in Control, LLC. All rights reserved.