T
Dear Experts,
We have a Metso Control valve with a positioner ND9206HE1. The positioner needs min 9.5V/20ma for operation and has a resistance of 475ohm.
The DCS open loop voltage is 21.9V. When the signal cables are connected to the positioner, it drops to 9.1V. Is this normal? Our Instrument team says that with 9.1V , this valve will not function properly.
The cables are OK because, I removed the positioner from field and connected it directly to our DCS FTA.
When I give 0% (4ma), voltage across positioner is 9V
When I give 100% (20ma), voltage across positioner is 9.35V
Open loop voltage of DCS signal wires is 21.9V
Or do you suspect if there is any problem with DCS power supply?
Another doubt which I have is , considering the positioner as a 475ohm resistor, at 4ma the voltage drop across it should be 4mA x 470 = 1.9V whereas in reality voltage is 9V. How is this possible.
regards,
tomsci
tomsci [at] gmail.com
regards,
tomsci