Hello,
recently there were quite a few very informative threads about control valve positioners, especially this one: http://control.com/thread/1026232438#1257611103.
Few days ago, we have mounted positioner on one control valve in our plant. Positioner is very simple, it has two wires for control signal reference (4...20mA), two other inputs for signaling end positions and additional two wires for actual position. It is fail safe design, which means that air (4 bar) is used to close the valve while, springs are used to open it. This way, in case of air is gone, valve will be fully opened.
So far everything seems normal (it is not used in actual application yet, but will when overhaul is finished), but I have one doubt. When going through all parameters, I have noticed that it has an option to choose valve characteristic (linear, equal percentage etc.).
Default option is linear and that is how it is set. However a mechanics guy told me that characteristic of a valve is more likely equal percentage.
My other colleague told me that it doesn't matter, when in closed loop control, it will find optimal position to control the flow. The only difference would be in speed of moving(!?!)
I'm not sure that this doesn't matter (there is an option in the positioner, after all). I wonder what I might expect in case that valve is equal percentage and positioner is set to linear.
Thank you
recently there were quite a few very informative threads about control valve positioners, especially this one: http://control.com/thread/1026232438#1257611103.
Few days ago, we have mounted positioner on one control valve in our plant. Positioner is very simple, it has two wires for control signal reference (4...20mA), two other inputs for signaling end positions and additional two wires for actual position. It is fail safe design, which means that air (4 bar) is used to close the valve while, springs are used to open it. This way, in case of air is gone, valve will be fully opened.
So far everything seems normal (it is not used in actual application yet, but will when overhaul is finished), but I have one doubt. When going through all parameters, I have noticed that it has an option to choose valve characteristic (linear, equal percentage etc.).
Default option is linear and that is how it is set. However a mechanics guy told me that characteristic of a valve is more likely equal percentage.
My other colleague told me that it doesn't matter, when in closed loop control, it will find optimal position to control the flow. The only difference would be in speed of moving(!?!)
I'm not sure that this doesn't matter (there is an option in the positioner, after all). I wonder what I might expect in case that valve is equal percentage and positioner is set to linear.
Thank you