Mark V, IOMA Power supply out of limit

G

Thread Starter

G.Rajesh

Our one of Frame-9E machine with Mark V control system is under major inspection. We are receiving the following alarm in <I>

1. IOMA power supply out of limits, P 335
2. IOMA power supply out of limits, P 24
3. TCD1 plug J01 is disconnected
4. TCD1 plug J02 is disconnected

and in processor <R> the following errors are appearing
1. I/O CONF RESET # 4
2. DCC ERRORS

We are expecting your suggestion and advice
 
G
Rajesh,

look up MKV diagnostic alarm (F:\Unit*\PROM\HELP_BD or QD) 273 - 277. It provides explanation & instruction for adjusting the IOMA power supply. Follow the instruction and the tolerance for best results.

Greg Ponto
Lead Combustion Turbine Specialist
Elwood Energy
greg.ponto [at] dom.com
 
You didn't mention what processor but having errors on <R> could indicate it's from <R> processor. Try adjusting the P5 pot in the power supply of that processor in slot 5 TCPS. Reset the errors on the processor. You don't use 335 volt sensors on 9E machine.
 