Posted by Miguel Hidalgo on 27 February, 2010 - 1:30 pm
I want to talk to a Zelio Logic Relay with the SR3-NET01BD Ethernet/Modbus module using the PC and VB.NET to control and know the status of a network of Zelios controlling Air Conditioning Units and pumps. Currently the Zelios are independent units automating and controlling the AC Units and pumps. We want to interconnecting to a Master (PC) or web app. so they can be monitored and control remotely through TCP/IP. The only info I found about the Zelios is the Functions 3, 6, 16 and 43 for a Twido to communicate with them. We need control as masters!

Any idea, sample code, etc.

Thank You! from Nicaragua

Miguel Hidalgo


Posted by Dan on 24 March, 2010 - 9:15 am
Modbus Function code 16 writes to a slave.

-----------
from the MODBUS APPLICATION PROTOCOL SPECIFICATION V1.1b:

6.12 16 (0x10) Write Multiple registers

This function code is used to write a block of contiguous registers (1 to 123 registers) in a remote device.

The requested written values are specified in the request data field. Data is packed as two bytes per register.

The normal response returns the function code, starting address, and quantity of registers written.
----------------

The Zelio devices are Modbus Slaves. Your PC is the Modbus master.

If you don't want to write your own HMI program that acts as the Modbus Master, there are literally hundreds of HMI/SCADA/DAQ PC software programs with (sometimes optional) Modbus drivers whose purpose in life is to read data from and write data to field devices.

Many of these HMI/SCADA/DAQ programs function as an OPC client, which uses a separate, (usually licensed) OPC server program to do the Modbus communications with the field device.

You might start with Zelio's manufacturer or try our best friend, Google. LabView finds wide use in academic settings.


Posted by mahdi on 2 February, 2012 - 11:27 am
hi

could you please tell me how can i read data from zelio with modbus module by HMI.


Posted by henneuse alain on 19 July, 2012 - 10:11 am
Zelio use Word %MW16 to %MW19 in R/W and %MW20 to %MW23 in R only

Use my soft for hmi to android

https://play.google.com/store/apps/details?id=zelioid_lite.projet&a mp;feature=search_result#?t=W10.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
A banker is a fellow who lends you his umbrella when the sun is shining
and wants it back the minute it begins to rain.
-- Mark Twain
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive