H
Dear experts,
we have Bailey infi-90 DCS System ,its termination Units for digital inputs from field are connected from a 24VDC floating power supply(-12/+12 VDC). suddenly many modules failed and we got a ground fault and burn cards on their -ve side power supply and we found the power supply became +11/+35 VDC instead of -12/+12 VDC. the power supplies are four each are connected together in redundant configuration.
we found one of these 4 power supplies not working and I expect it may be the cause of the DCS module failures as there is high power came to the -ve side of the DCS Termination units but can this happen for a floating power supply who suppose to give -12/+12 VDC to give for example +11/+35??
this problem caused many DCS digital input channels to fail on short circuit and the high +ve power to go to the -ve side through the short circuit defect DCS digital input module and the closed field dry contact.
can Infi-90 DCS digital input channels failed on short circuit??
also can floating power supply (-12/+12)fail giving high +ve power on the -ve side???
thank you ...
thank you ...