6.9KV Vacuum circuit breaker rack in/rack out procedure
Engineering and workplace issues. topic
Posted by KKK on 17 February, 2011 - 4:26 am
Dear Gents,

I have prepared the 6.9KV vacuum circuit breaker rack in/rack out procedure, I request you to kindly give your inputs to safe guard the personal to prevent hazards associated with rack in /rack out circuit breakers

Earlier we are rack in/rack out the breaker with the compartment door open, now we have modified the door & now we are able to rack in/rack out with compartment door closed

6.9KV Rack in Procedure

1. Identify the correct Breaker

2. Check Breaker visually for cluster condition, left out tools or any other external materials

3. Check the breaker is open & spring is fully discharged

4. Check the breaker is on local mode

5. Ensure that breaker control supply is switched off

6. Place the breaker in the compartment in test position & insert the breaker control supply plug

7. Close the breaker compartment door

8. Rack in the breaker

9. Open the breaker compartment door & check that breaker is in "connect" position & spring is in discharged condition

10. Close the breaker compartment door

11. Switch on the breaker control supply (MCCB#02)

12. Select the breaker in Remote mode

Breaker Rack out procedure

1. Identify the correct breaker

2. Confirm the breaker is open

3. Select the breaker in Local mode

4. Rack-out the breaker with the compartment door closed

5. Switch off the control supply (MCCB#02)

6. Open the breaker compartment door, ensure that the breaker is in test position, also check the breaker indication "Dis-connect" at local

7. Remove the control supply plug

8. Discharge the spring

9. Close the breaker compartment door


Posted by William \(Bill\) L Mostia Jr PE on 19 February, 2011 - 3:10 pm
I am not a heavy electrical guy but it would appear that consideration of personal protection equipment (PPE) has been left out. See link below to see how PPE is important.

http://www.youtube.com/watch?v=m_e48IP098U&feature=related

Have you considered NFPA 70E requirements in this regard or equivalent?

http://www.arcflash.me/nfpa-70e-arc-flash-code.php

Dealing with heavy duty electrical stuff isn't for amateurs. Have your procedure reviewed by a qualified and competent electrical engineer in high voltage electrical systems.

William (Bill) L. Mostia, Jr. PE
Sr. Consultant
SIS-TECH Solutions, LP

Any information is provided on Caveat Emptor basis.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Hindsight is an exact science.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive