We have two GE PG5371 gas turbine at fertilizer complex in Pakistan. each having ISO rating capacity of 26.3Mw. controlling system is MARK V & both turbine are operate on synchronized state with combine cycle ON mode. at combine cycle ON IGVs opening reduced to 56% & becomes fixed by default. total plant load active power demand is 20Mw . each gas turbine shared the 10Mw With exhaust temp 405 & 420C respectively at 56% IGVs opening , 10Mw load.
Now our aim is to review & increase the exhaust temp to 10 to 15C more by reducing further IGVs opening from 56% angle to 52% so that in HRSG steam generation can be increased. Now what you suggest new opening & how we can make it safe for max exhaust temp increasing. Especially is there any chance to of compressor stall & surging if we go to reduce 4% more IGVs opening . If it is, then how by which mean we can find out new safe opening.
Exhaust tripping temp is 570C that is far away from normal operated value. Our gas turbine IGVs range is 42 to 85 degree.
Plz respond also of the other GE Frame 5 machine about the IGVs opening & exhaust temp in combine cycle On mode.
Thank you
Now our aim is to review & increase the exhaust temp to 10 to 15C more by reducing further IGVs opening from 56% angle to 52% so that in HRSG steam generation can be increased. Now what you suggest new opening & how we can make it safe for max exhaust temp increasing. Especially is there any chance to of compressor stall & surging if we go to reduce 4% more IGVs opening . If it is, then how by which mean we can find out new safe opening.
Exhaust tripping temp is 570C that is far away from normal operated value. Our gas turbine IGVs range is 42 to 85 degree.
Plz respond also of the other GE Frame 5 machine about the IGVs opening & exhaust temp in combine cycle On mode.
Thank you