R
Hi every body,
In our power plant, there are two GE FRAME 9E gas turbine with MKV TMR.I have noticed the power supply data from DIAGC DATA display - TCQAG1B for core R are as follow:<pre>
P5v = 5.11 vdc
P15a = - 0.12 vdc ( JE - 29 = -0.02 )
N15a = 17.09 vdc ( 30 = 3.00 )
P15b = 9.45 vdc ( 31 = 1.55 )
N15b = -17.1 vdc ( 32 = -3.00 )
P125v= 1.98 vdc ( 33 = 0.04 )
N125v= 152.89 vdc ( 34 = 3.00 )
Also the power supply values of IOMA for same core are:
P5- voltage = 0.00v
P15- voltage = 29.2v
N15- voltage = 0.00v
P24- voltage = 14.2v
N24- voltage = -14.3v
DCOM- voltage = 1.3 v</pre>
While S&T are normal.
I did the following procedures :
1.Replacing TCPS of core R without result.
2.Replacing TCQA no result.
3.Replacing TCQC no result.
4.Replacing SDCC & SLCC no result.
5.I swapping SDCC & SLCC of core T with core R,so the problem had transferred to core T, and all above voltages were correct at core R, but status of both cores was A6. so I returned each core to its place.
6.Replacing EEPROMEs of SDCC (DS200GHDQF1CBG 01&2) WITHOUT RESULT.
The diagnostic alarm is:
IOMA power supply out of limit, P5, P24, P15, N24, N15, DCOM.
There is no 125 v dc battery ground, and the voltages are +65.44 v & -65.4 v at core PD.
Also no difficulties, intermittent with the operation of the unit > So pls any solution for this problem.
In our power plant, there are two GE FRAME 9E gas turbine with MKV TMR.I have noticed the power supply data from DIAGC DATA display - TCQAG1B for core R are as follow:<pre>
P5v = 5.11 vdc
P15a = - 0.12 vdc ( JE - 29 = -0.02 )
N15a = 17.09 vdc ( 30 = 3.00 )
P15b = 9.45 vdc ( 31 = 1.55 )
N15b = -17.1 vdc ( 32 = -3.00 )
P125v= 1.98 vdc ( 33 = 0.04 )
N125v= 152.89 vdc ( 34 = 3.00 )
Also the power supply values of IOMA for same core are:
P5- voltage = 0.00v
P15- voltage = 29.2v
N15- voltage = 0.00v
P24- voltage = 14.2v
N24- voltage = -14.3v
DCOM- voltage = 1.3 v</pre>
While S&T are normal.
I did the following procedures :
1.Replacing TCPS of core R without result.
2.Replacing TCQA no result.
3.Replacing TCQC no result.
4.Replacing SDCC & SLCC no result.
5.I swapping SDCC & SLCC of core T with core R,so the problem had transferred to core T, and all above voltages were correct at core R, but status of both cores was A6. so I returned each core to its place.
6.Replacing EEPROMEs of SDCC (DS200GHDQF1CBG 01&2) WITHOUT RESULT.
The diagnostic alarm is:
IOMA power supply out of limit, P5, P24, P15, N24, N15, DCOM.
There is no 125 v dc battery ground, and the voltages are +65.44 v & -65.4 v at core PD.
Also no difficulties, intermittent with the operation of the unit > So pls any solution for this problem.