Allen Bradley 1974-IRT8/B module failure

A

Thread Starter

Abfuta

We are experiencing a strange failure in FLEX I/O Non-Isolated Thermocouple/RTD/mV modules 1974-IRT8/B. these modules have a communication with Control logix 5561 PLC by means of ControlNet adapter module ( 1794-ACNR15 ). we checked the RTD wires and power many times before replacing the modules but without success.

The failed module have a green power led on indication and with a permanent red led on channel 0.

Anyone know what the cause of module failure could be? has anyone experienced this before?
 
> Have you set the run bit for the DeviceNet scanner?
> Local:X:O.CommandRegister.Run

Thank you for the reply,
the run bit do the job even in ControlNet communications? because I didn't specify that we don't have DeviceNet, I'll post feedback later ..
 
Ok, I can confirm that this bit "Local:X:O.CommandRegister.Run" doesn't exist in controller tag, but I heard that AB IRT modules manufactured between January 1, 2010 and May 31, 2010 has a potential anomaly, can anyone confirm this?
 
Top