mohsen_mazarei

Hi
I have a Redundancy Automation system with cpus 417-4H Siemens. in my Plant there are safety modules. I have a problem with safety signals. when I download my Pcs7 program to cpus, cpu in rack1 stops and when I restart it, The cpu don't read the safety signals, but cpu in rack0 read all signals and work correctly. Please help me about this problem.

in diagnostic buffer:
Event 12 of 94: Event ID 16# 75DD
Safety Program: Shutdown of a Failsafe Runtime Group active
The RTG_LOGIC DB 3191 detected a failure in a F Runtime group
Internal Error ID 1: 0
Internal Error ID 2: 0
Internal error, Incoming event
12:33:56:569 am 01/01/94


Event 13 of 94: Event ID 16# 75DE
Safety Program: Full Shutdown of the F-Program active
Internal Error ID 1: 0
Internal error, Incoming event
12:33:56:569 am 01/01/94


Event 14 of 94: Event ID 16# 75E1
Safety Program: Error in the F_TESTC Detected
Runtime group with the failed F-FB will be disabled.
Instance DB number of F-FB with failure: 3188
Internal Error ID 1: 12
Internal error, Incoming event
12:33:56:351 am 01/01/94

also full diagnostic buffer messages is attached.

Thanks a lot.
 
Hello;

Just to make things clear, you are using a redundant S7-400H system in which you would like to run Safety programs and IOs. Correct?
Do you have a safety program (with safety software) on those PLCs? Siemens refers to this as a S7-400FH system, and, yes, and additional license is required, along with the software. The messages you receive would be linked to an unauthorized use of F-blocks in your program.

Please have a look at the S7-400H/FH configuring and programming manual; it will make many issues clearer. You can download it from the Siemens support site:
http://support.automation.siemens.com/WW/view/en/2201072

Hope this helps,
Daniel Chartier
 