I've been using 3-wire 100 ohm platinum RTDs for years. Most have been wired to recorders, recorder/controllers or PLCs.
Having to adjust a recorder's input offset a little has been common (we used calibrated mercury in glass thermometers as a reference), but when one requires more than maybe a 2 or 3 degree correction, I get nervous. More than that and I start looking for a problem. Lead lengths are generally 100 feet or less, with the shield grounded at the instrument.
At my new location, I've already encountered 3 RTDs feeding ABB 250 DIN controllers and all three have large offsets entered to get them to match the nearest thermometer.(14+ degrees on two of them!) Measured temps are 220 to 250 degf, and RTDs are in thermowells.
I've only had access to one machine, and only briefly. The controller is perfect with an RTD simulator attached locally, and I swapped out the RTD. The lead is only about 25 feet long, and I couldn't check it or replace it (yet). Problem could be an ill-sized RTD or other thermowell related problem. Don't know yet.
Question: Is there any valid justification for a 14 degree offset? Is this typical of these DIN controllers?
Having to adjust a recorder's input offset a little has been common (we used calibrated mercury in glass thermometers as a reference), but when one requires more than maybe a 2 or 3 degree correction, I get nervous. More than that and I start looking for a problem. Lead lengths are generally 100 feet or less, with the shield grounded at the instrument.
At my new location, I've already encountered 3 RTDs feeding ABB 250 DIN controllers and all three have large offsets entered to get them to match the nearest thermometer.(14+ degrees on two of them!) Measured temps are 220 to 250 degf, and RTDs are in thermowells.
I've only had access to one machine, and only briefly. The controller is perfect with an RTD simulator attached locally, and I swapped out the RTD. The lead is only about 25 feet long, and I couldn't check it or replace it (yet). Problem could be an ill-sized RTD or other thermowell related problem. Don't know yet.
Question: Is there any valid justification for a 14 degree offset? Is this typical of these DIN controllers?