Regarding HGPI for Gas Turbine Frame 5

V

Thread Starter

vkumar

We have captive power plant with two frame 5 Gas Turbine in which one is standby. The Combustion inspection was done at 8000 hrs. one machine is running at 14,000 hrs. Please advice whether we can go for Hot gas path inspection at 18,000 or earlier as this is a refurbished machine. The machine is running on single fuel, i.e natural gas. The advice would be highly appreciated.
 
You need to obtain a copy of GER-3620. It details all the considerations which need to be evaluated in the decision to conduct preventive maintenance of GE-design heavy duty gas turbines.
 
Maybe you can compare it with the O&M GE that you have in the MAJOR FACTORS INFLUENCING MAINTENANCE AND EQUIPMENT LIFE section, because from there you can get a comparison
 