Hi,
Need Help about the Trip Log program.
On one GT the HMI is configured with Speedtronic Mark 5 TMR
Windows 4
TCI and Cimplicity

The problem is that during the GT trip, the Trip History program doesn't capture all the parameters just only a few. and really the GT is running above 80% TNH.

On the output file we found all the alarms, and the 64 parameters but a few with indication and others no indication

Thanks for you help
my email if need more information
[email protected]
 
B

Bob Johnston

The first question is the usual one, did this suddenly happen, have you made any software changes recently or has this always been happening? I would suggest that firstly you reset the Trip History settings, there is a good guide in GEH 6126A, the HMI Application Manual. Once you have done this and still have a problem, get back to us. A print of the Trip History log file would be useful.
 
It is suspicious that the unit is above 80% speed, but you probably didn't tell us that this is a two-shaft or aero-derivative unit.

Please provide an example of no data by posting the "empty" Trip History.
 
D
Hi Bob Johnston
Hi CSA,

Thanks for your answers ;

No this is done only when the trip occurs
No any software changed recently

Tel me please how to firstly reset the Trip History settings,

I will try to see the guide GEH 6126A, the HMI Application Manual.

The GT is very far to my office I will try this work next weeks and inform you.

Tel me please how to send you all the text files about the past trips

To CSA :
No suspicious I just wanted to inform you that the GT is running when I said 80% of speed. Yes this GT is a two-shaft aero-derivative unit.
LM2500 +PGT25.

Send me your email or how to send you theses files