We are using MarkV in frame 6b GE machine. IGV LVDTs are connected in 17, 18 and 19, 20 terminals respectively in TBQC terminal board. We found 19, 20 terminal showing abnormal value that means CSGV_B = 7.9 when we connect any LVDT in those terminals. But the other terminals work fine and shows CSGV=34 deg.
Then we wanted to change the terminal position 21, 22 for LVDT 1 and 23,24 for LVDT 2 to configure servo output 6 for IGV. We did as follows:
1. We configured CSGV from Q_R_POS09 to Q_R_POS11 and CSGV_B from Q_R_POS10 to Q_R_POS12 and CAGV from Q_Q_SV05 to Q_Q_SV06, CSRGVOUT from Q_Q_SV05 to Q_Q_SV06 in IO.ASG.
2. Then we modified ACALIB.DAT file by making same all fields of servo output 06 from servo output 05 (assigned for IGV).
3. At IO_CFG we modified TCQA card definition and for servo output no. 05 we put Function type and sub-type: 00 and for servo output no. 06 we put 43. Then we put all other values in servo 06 following servo no. 05.
4. Then we downloaded IO_CFG in <R>, <S>, <T> processors and rebooted one by one.
5. After this modification autocalibration and manual calibration works fine.
But the problem is:
1. INLET GUIDE VANE CONTROL TROUBLE ALARM
2. INLET GUIDE POSITION SERVO TROUBLE ALARM
this two alarms are still there even we do master reset.
Then we tried to find the cause of these two alarms: in rung no. SEQ_TRB2 101 we found CSRGVOUT=0 and CSR17CMP=34 at normal condition.
Is there any mistake during the software modification? For this modification do we need to download USER to r, s and t?
Then we wanted to change the terminal position 21, 22 for LVDT 1 and 23,24 for LVDT 2 to configure servo output 6 for IGV. We did as follows:
1. We configured CSGV from Q_R_POS09 to Q_R_POS11 and CSGV_B from Q_R_POS10 to Q_R_POS12 and CAGV from Q_Q_SV05 to Q_Q_SV06, CSRGVOUT from Q_Q_SV05 to Q_Q_SV06 in IO.ASG.
2. Then we modified ACALIB.DAT file by making same all fields of servo output 06 from servo output 05 (assigned for IGV).
3. At IO_CFG we modified TCQA card definition and for servo output no. 05 we put Function type and sub-type: 00 and for servo output no. 06 we put 43. Then we put all other values in servo 06 following servo no. 05.
4. Then we downloaded IO_CFG in <R>, <S>, <T> processors and rebooted one by one.
5. After this modification autocalibration and manual calibration works fine.
But the problem is:
1. INLET GUIDE VANE CONTROL TROUBLE ALARM
2. INLET GUIDE POSITION SERVO TROUBLE ALARM
this two alarms are still there even we do master reset.
Then we tried to find the cause of these two alarms: in rung no. SEQ_TRB2 101 we found CSRGVOUT=0 and CSR17CMP=34 at normal condition.
Is there any mistake during the software modification? For this modification do we need to download USER to r, s and t?