C
Hi everybody,
Our gaz turbine (9001E) tripped by loss of flame two times at 25MW.
We suspected at first the servo valve (65FP) and
we changed it by a new one.
After the second test the turbine was fine, but many hours of work it retripped at 50 MW by the same cause (loss of flame).
We already launched a trend to troubleshoot the case. Some one of GE recommend to change the Liquid Fuel Stop Valve Limit Switch (33fl) (I wasn't there so I don't know why) and they changed it.
At the third test it seemed good but after many hours of working it retripped again at 90MW.
By checking the second trend (90MW trip), I observed that:
-33FL toggled "from false to true" at the same time with [< fqrout "from 66 to -25%"
<Liquid Fuel Stop Valve Control Signal Time Delayed "from true to false" at (12:58:41.7)
but the Master protective signal toggled (L4) toggled "from true to false" at 12:58:42.1,.
Can what happened be due to a problem in the stop valve (VS1)? or to the new 33FL? (we make also in the trend signal of battery ground and +/-Leg 125VDC Bus Level and +&- 125VDC Ground but there were some smal fluctuation just after the trip.
-I need your help to resolve this problem.
-I don't know what's the role of l20FLXX can you explain to me?
Best regards
Our gaz turbine (9001E) tripped by loss of flame two times at 25MW.
We suspected at first the servo valve (65FP) and
we changed it by a new one.
After the second test the turbine was fine, but many hours of work it retripped at 50 MW by the same cause (loss of flame).
We already launched a trend to troubleshoot the case. Some one of GE recommend to change the Liquid Fuel Stop Valve Limit Switch (33fl) (I wasn't there so I don't know why) and they changed it.
At the third test it seemed good but after many hours of working it retripped again at 90MW.
By checking the second trend (90MW trip), I observed that:
-33FL toggled "from false to true" at the same time with [< fqrout "from 66 to -25%"
<Liquid Fuel Stop Valve Control Signal Time Delayed "from true to false" at (12:58:41.7)
but the Master protective signal toggled (L4) toggled "from true to false" at 12:58:42.1,.
Can what happened be due to a problem in the stop valve (VS1)? or to the new 33FL? (we make also in the trend signal of battery ground and +/-Leg 125VDC Bus Level and +&- 125VDC Ground but there were some smal fluctuation just after the trip.
-I need your help to resolve this problem.
-I don't know what's the role of l20FLXX can you explain to me?
Best regards