Hi all;
We have two 7FA's on site and currently have a problem with one them tripping on high exhaust pressure. I have pulled a trend from the transmitter and it looks like the pressure is spiking every few minutes. Normally the pressure runs around 9 inH20 at base load but like I said spikes every 10 or 15 minutes. Because the transmitter shows the spike and the switches also show the spike I believe it is a real pressure. This has always been an issue but seems to be worse right now.
GE's response was to check the slope of the tubing and to change it to larger tubing. I have changed the slope of the tubing and moved from 1/4" to 3/8" but am still seeing the issue. I have also been told by a TA to try heat tracing the tubing as moisture could be freezing up and flashing off into steam. I have not heat traced the tubing yet as the spikes are evident when the temperature was well above freezing. The last two trips were below freezing though. Both of the units pressure spike but one seems to have higher spikes than the other.
What else could be causing this pressure spike? Or what else should I check. I am having a hard time believing it is the tubing, or that heat tracing would help.
We have two 7FA's on site and currently have a problem with one them tripping on high exhaust pressure. I have pulled a trend from the transmitter and it looks like the pressure is spiking every few minutes. Normally the pressure runs around 9 inH20 at base load but like I said spikes every 10 or 15 minutes. Because the transmitter shows the spike and the switches also show the spike I believe it is a real pressure. This has always been an issue but seems to be worse right now.
GE's response was to check the slope of the tubing and to change it to larger tubing. I have changed the slope of the tubing and moved from 1/4" to 3/8" but am still seeing the issue. I have also been told by a TA to try heat tracing the tubing as moisture could be freezing up and flashing off into steam. I have not heat traced the tubing yet as the spikes are evident when the temperature was well above freezing. The last two trips were below freezing though. Both of the units pressure spike but one seems to have higher spikes than the other.
What else could be causing this pressure spike? Or what else should I check. I am having a hard time believing it is the tubing, or that heat tracing would help.