In old site we have Telemecanique Modicon TSX Micro plc (TSX3710001) where we need extend with SCADA system & GSM modem (sending SMS with fault).

Application - water treatment, max I/O 100, analog input max 8.
There some option for new SCADA (what i got from net).

OPTION1:
Use PC with touch screen, connection cable (TSXCUSB485 + TSXCRJMD25) or TSXPCX3030 (PLC - PC), Setup PLC to UNI-TELWAY LINK master protocol, Run OPC Factory Server and SCADA software on PC.

OPTION2:
Use Schneider 10.4 Magelis Touch Screen XBTGT5230, connection cable XBTZ968 (MAGELIS - PLC).
-----------------------------------------------------------------------

Questions:

Option1.
Q1) - May you recommend some low-cost SCADA for this application?
Q2) - What kind GSM modem I need, where I connect and how setup?

Option2.
Q3 - What protocol needs to be setup ? (UNI-TELWAY or modbus RTU)?

Q4) - What kind GSM modem I need, where I connect and how setup?

Q5) - Is it possible to archive the trend (levels, flow) and show in Magelis touch screen for longer time or this is only HMI for simple task (start, stop, change mode, setup levels, ...) ?
 
> Q1) - May you recommend some low-cost SCADA for this application?
http://pvbrowser.org


> Q2) - What kind GSM modem I need, where I connect and how setup?
http://www.violasystems.de/content/view/20/44/

> Option2.
> Q3 - What protocol needs to be setup? (UNI-TELWAY or modbus RTU)?
Would prefer Modbus either RTU or TCP

> Q4) - What kind GSM modem I need, where I connect and how setup?
See Q2

> Q5) - Is it possible to archive the trend (levels, flow) and show in Magelis
> touch screen for longer time or this is only HMI for simple task (start, stop,
> change mode, setup levels, ...)?
Not needed.
Use standard PC hardware.

Yes it es possible to archive either in files or database systems with SQL.
 