We are facing VCMI card related problem frequently in our GT-1 machine. Give us advice to resolve this type of problem permanently. The problems are described as below
On 27/11/2011 night at 9.30 pm GT1 Trip on "GCV NOT FOLLOWING REF. TRIP" before few second one diagnostic alarm came i.e "P 428 (Y) XVPROS8S02_A DIGNOSTIC ALARM" on hmi. After that we make master reset , at zero speed of turbine ready to start came so machine started.
At on 28/11/2011 morning at approx 9.30 am machine trip on same alarm as above. we observed GCV ref and position having 10 difference. so we are trying to calibarate GCV as per manual 2 procedure.
But in that Min pos and MAX pos is done and fix it. After that push calibrate button but GCV is not open/close automatically. so, we are taking shutdown of G1 mark vi. and restart it but all 3 processor showing BOOT mode only and at mark vi all processor GREEN led blink at a time.
Then we check diagnostic alarm in VCMI card in m6b file. we found in T rack VCMI card having fault code 46,50 persist with 1 state. so we swap the T rack vcmi card with S rack. so diagnostic alarm of T rack reset and set in S rack. so we concluded that VCMI card of T rack was faulty. so we replace T rack card with new one on dated 08/12/2011.and in S rack original card insert.
T rack download configuration and reboot all processor. so VCMI diagnostic was reset. and all three controller come out form boot mode to normal. m6b file sho was equal and normal.
1) so we start GT, it was running normal with no fault code in VCMI card.
2) After two days on dated 11/12/2011, again problem was observed in “S” processor with VCMI card diagnostic alarm having fault code 47, 51 in m6b file. But machine was running normal with VCMI fault code.
3) On dated 20/12/2011 evening machine was trip on "GCV not following ref. trip" After zero speed we check the VCMI diagnostic alarm was reset. We check in all. VCMI card having no diagnostic alarm in m6b file. In field LED status of all VCMI card was found OK. So we start the machine and take the load on machine.
4) From 20/12/2011 evening to 24/01/2012 morning GT-1 machine was running normal without any diagnostic alarm in all three VCMI card.
5) on 24/01/2012 morning 8.34 AM the VCMI diagnostic alarm was observed in “S” processor with fault code 47,51 in m6b file. M6b file showing equal.
6) so we take the shutdown the machine and power off the "s" rack power. Take out VCMI card and cleaning the card and its slot. After that re-insert the card and power on. VCMI alarm get reseted. so we start the machine on 29/01/2012.
7) again on 04/02/2012 00.00 hrs VCMI "s" diagnostic alarm came and automatically reset. At 2.30am same alarm came and machine was trip on "GCV NOT FOLLOWING REF."
Still VCMI "S" diagnostic alarm persist. Its fault code was 47,51.
We observed that whenever VCMI diagnostic alarm was persist, after few days the machine was trip on "GCV NOT FOLLOWING REF. TRIP".
On 27/11/2011 night at 9.30 pm GT1 Trip on "GCV NOT FOLLOWING REF. TRIP" before few second one diagnostic alarm came i.e "P 428 (Y) XVPROS8S02_A DIGNOSTIC ALARM" on hmi. After that we make master reset , at zero speed of turbine ready to start came so machine started.
At on 28/11/2011 morning at approx 9.30 am machine trip on same alarm as above. we observed GCV ref and position having 10 difference. so we are trying to calibarate GCV as per manual 2 procedure.
But in that Min pos and MAX pos is done and fix it. After that push calibrate button but GCV is not open/close automatically. so, we are taking shutdown of G1 mark vi. and restart it but all 3 processor showing BOOT mode only and at mark vi all processor GREEN led blink at a time.
Then we check diagnostic alarm in VCMI card in m6b file. we found in T rack VCMI card having fault code 46,50 persist with 1 state. so we swap the T rack vcmi card with S rack. so diagnostic alarm of T rack reset and set in S rack. so we concluded that VCMI card of T rack was faulty. so we replace T rack card with new one on dated 08/12/2011.and in S rack original card insert.
T rack download configuration and reboot all processor. so VCMI diagnostic was reset. and all three controller come out form boot mode to normal. m6b file sho was equal and normal.
1) so we start GT, it was running normal with no fault code in VCMI card.
2) After two days on dated 11/12/2011, again problem was observed in “S” processor with VCMI card diagnostic alarm having fault code 47, 51 in m6b file. But machine was running normal with VCMI fault code.
3) On dated 20/12/2011 evening machine was trip on "GCV not following ref. trip" After zero speed we check the VCMI diagnostic alarm was reset. We check in all. VCMI card having no diagnostic alarm in m6b file. In field LED status of all VCMI card was found OK. So we start the machine and take the load on machine.
4) From 20/12/2011 evening to 24/01/2012 morning GT-1 machine was running normal without any diagnostic alarm in all three VCMI card.
5) on 24/01/2012 morning 8.34 AM the VCMI diagnostic alarm was observed in “S” processor with fault code 47,51 in m6b file. M6b file showing equal.
6) so we take the shutdown the machine and power off the "s" rack power. Take out VCMI card and cleaning the card and its slot. After that re-insert the card and power on. VCMI alarm get reseted. so we start the machine on 29/01/2012.
7) again on 04/02/2012 00.00 hrs VCMI "s" diagnostic alarm came and automatically reset. At 2.30am same alarm came and machine was trip on "GCV NOT FOLLOWING REF."
Still VCMI "S" diagnostic alarm persist. Its fault code was 47,51.
We observed that whenever VCMI diagnostic alarm was persist, after few days the machine was trip on "GCV NOT FOLLOWING REF. TRIP".