1
When we parallel to the grid after 2 minutes or so the 100 A breakers drop out. We have only been outputting around 1 ~4 kW.
If we manually drop the breaker there seems to be almost no load change on the generator (so the 1~4 kW seems right), but our CT's are all measuring up around 90~100 A?
How is this possible? We tried our free excitation voltage at 237V and 243V to see if this would make a difference (on a 240 V phase-N) grid, with no change.
If we manually drop the breaker there seems to be almost no load change on the generator (so the 1~4 kW seems right), but our CT's are all measuring up around 90~100 A?
How is this possible? We tried our free excitation voltage at 237V and 243V to see if this would make a difference (on a 240 V phase-N) grid, with no change.