Myth 1 - "It is possible for generators connected to the grid to operate in different frequencies (small of large) for the Entire Operation Period/Sustained Periods of time "
Fact - "NO, generators connected to the grid CANNOT OPERATE AT DIFFERENT FREQUENCIES for sustained periods of time "
Explanation - There will be small frequency deviation around a particular value. AT ONE TIME INSTANT OR A SNAPSHOT it will look like the generators are operating in different frequencies BUT the generators or group of generators hunt "AROUND" a frequency value. This swinging of generators in one area with generators of the other area is called "low frequency oscillation" or "Interarea oscillation". The Magnitude of frequency hunting may vary from 0.1 - 0.5 hz (at any one given time instant). The power flow change will depend on the gird size, the generator group, the load state, etc. typically this low frequency load hunting can range from 50MW to 200 MW. It is possible for Inter-area oscillations to continue for sustained periods of time, but this DOES NOT MEAN THAT THE group of generators are out of sync with each other. The article explains below how interarea oscillation occur and how they are controlled with PSS.
Paper on interarea occilations - http://www.2shared.com/document/Eya2tNK0/interarea_occilations.html
Fact - "NO, generators connected to the grid CANNOT OPERATE AT DIFFERENT FREQUENCIES for sustained periods of time "
Explanation - There will be small frequency deviation around a particular value. AT ONE TIME INSTANT OR A SNAPSHOT it will look like the generators are operating in different frequencies BUT the generators or group of generators hunt "AROUND" a frequency value. This swinging of generators in one area with generators of the other area is called "low frequency oscillation" or "Interarea oscillation". The Magnitude of frequency hunting may vary from 0.1 - 0.5 hz (at any one given time instant). The power flow change will depend on the gird size, the generator group, the load state, etc. typically this low frequency load hunting can range from 50MW to 200 MW. It is possible for Inter-area oscillations to continue for sustained periods of time, but this DOES NOT MEAN THAT THE group of generators are out of sync with each other. The article explains below how interarea oscillation occur and how they are controlled with PSS.
Paper on interarea occilations - http://www.2shared.com/document/Eya2tNK0/interarea_occilations.html