communication hangup ABB AC450 controller
PLCs and related questions. topic
Posted by paru on 20 May, 2012 - 2:00 am
we have communication between Siemens S7 PLC and ABB 450 through serial interface using card CI532 V03. We are facing sometimes that communication hangs up and is reset by using MDB MVI 1 in ABB PLC. We are not able to figure out the reason for it.


Posted by Rob on 22 May, 2012 - 9:10 am
> We are not able to figure out the reason for it.

And from that amount of information neither am I :)

First up - Is this a new problem? New Installation? Has anything changed?

Are you getting any errors reported by either controller? Connect control Builder to the AC450 and send the log messages to the screen.

What serial protocol are you using - Modbus or Siemens?

What are the indicator lights on the front of the CI532 doing. Do you get any activity at all when the link stops? Are there indicator lights on the S7?

What is the CPU load on your AC450?

Do you have a PC program controlling your CI532 interface? What happens if you Block/Reset that PC program? Does it restart the interface?

Rob
www[.]lymac.co.nz

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
The use of COBOL cripples the mind; its teaching should, therefore, be
regarded as a criminal offense.
-- E. W. Dijkstra
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive