from the Forum department...
modbus starting address question
Communications systems and equipment. topic
Posted by barramundi9 on 2 June, 2012 - 3:35 am
I am really new to modbus and trying to get information out of the meter mp-84dh which is modbus compliant.
Below is the code I found on the internet:
http://jalla.org/~stig/modbus/
int modbus_read_holding_registers(unsigned char slave_id,
unsigned int start_address, unsigned int num_registers,
unsigned short * modbus_registers)
unsigned char transmit[255];
transmit[0] = slave_id;
transmit[1] = MB_READ_HOLDING_REGISTERS;
transmit[2] = start_address >> 8;
transmit[3] = start_address & 0xFF;
transmit[4] = num_registers >> 8;
transmit[5] = num_registers & 0xFF;
short crc = CRC16(transmit, 6);
transmit[6] = crc;
transmit[7] = crc >> 8;
if (write(fd, transmit, 8) == -1) {
perror("Unable to write to serial device");
mb_datagram_status = MB_ERROR;
return -1;
mb_waiting_for_reply = 1;
struct timespec time;
clock_gettime(CLOCK_REALTIME, &time);
time.tv_sec += 1;
/* Time out here if no bytes have been received within the time out period */
if (pthread_cond_timedwait(&datagram_start_receiving,
&waiting_for_reply, &time) == ETIMEDOUT) {
mb_datagram_status = MB_TIMEOUT;
timeout_error_count++;
return -1;
pthread_cond_wait(&datagram_finished_receiving, &waiting_for_reply);
mb_waiting_for_reply = 0;
if (mb_datagram_status == MB_OK) {
unsigned char byte_count = modbus_read_num_bytes(datagram);
mb_datagram_status = MB_OK;
unsigned char * datagram_data = datagram + 3;
int i;
for(i = 0; i < byte_count / 2; i++) {
modbus_registers[i] = datagram_data[i * 2] << 8 | datagram_data[i * 2 + 1];
return byte_count / 2;
} else {
return mb_datagram_status;
And the spec on MP-84DH mentions the following:
Modbus Register Address
Address word item code
0000H 2 Watt Hour 03H
0002H 1 Watt 03H
0003H 1 Voltage 03H
0004H 1 Current 03H
I wrote:
readState = modbus_read_holding_registers(2, 0, 1, mbusRegisters);
printf("readState : %d\n", readState);
and readState returns -1 because it died at the block:
if (pthread_cond_timedwait(&datagram_start_receiving, &waiting_for_reply, &time) == ETIMEDOUT) {
return -1;
Have I given it the wrong starting address, according to spec, it looks like the starting address is 0, or am I misunderstanding something here?
Any help will be appreciated.
Thanks.
barramundi9
Posted by Helen on 4 June, 2012 - 1:42 am
It seems that you need swap bytes of CRC. The high byte should be first.
Also you may try to build and send this request a manually from Advanced Serial Port Monitor. It is possible the device returns an error code.
Posted by barramundi9 on 19 July, 2012 - 9:06 am
Hi Helen,
thanks for the reply, I know it's been a month ...
I tried swapping the crc bytes, but it still dies in
and returns -1
I used some modbus testing software and it does return the values I want.
Any ideas?
Posted by Andrzej on 21 July, 2012 - 9:01 am
Try connect to modbus slave simulator like Modsim to see the frame is send from application and compare this with the frame which is send from Modbus test application (like Modbus Tester from www.modbus.pl).
Andrzej
Posted by barramundi9 on 2 August, 2012 - 11:36 pm
Hi, thanks for the reply.
I've given up on this and use libmodbus instead.
www.libmodbus.org
And it works!!
Thank you.
barramundi9
Every improvement in communication makes the bore more terrible.
-- Frank Moore Colby
Advertise here
Advertisement
our advertisers