A
Does anyone have any advice on this.
I have been involved in commissioning some VSD drives on a ship. They are being used to control the starting and stopping of hydraulic power-packs and we have had loads of problems.
The layout is 2x75kw 1 x 90kW and 1 x 120kw drives connected to 3x230kW generators.
The generators are Hawker Siddley 415V sets built around 1979.
On initial start up with two generators connected starting any drive resulted in the busbar volts rising to 475V where we stopped the drive.
To get round this I reduced the VSD carrier frequency to .7kHz and this problem seemed to have sorted. Now the drives start up ok, but when loaded generators trip off line on reverse power. We are fairly sure the VSD's are not the problem and it's noise on the current waveform causing the reverse power relays to trip. Reverse power on these sets is by electronic means. There is a current shunt in one of the phases and compares the signal from this with phase voltage. The resultant lagging or leading dictates weather the set is generating or motoring.
The solution is to put by-pass contactors around the VSD's but this is not curing the problem.
Anyone any ideas?
Al
I have been involved in commissioning some VSD drives on a ship. They are being used to control the starting and stopping of hydraulic power-packs and we have had loads of problems.
The layout is 2x75kw 1 x 90kW and 1 x 120kw drives connected to 3x230kW generators.
The generators are Hawker Siddley 415V sets built around 1979.
On initial start up with two generators connected starting any drive resulted in the busbar volts rising to 475V where we stopped the drive.
To get round this I reduced the VSD carrier frequency to .7kHz and this problem seemed to have sorted. Now the drives start up ok, but when loaded generators trip off line on reverse power. We are fairly sure the VSD's are not the problem and it's noise on the current waveform causing the reverse power relays to trip. Reverse power on these sets is by electronic means. There is a current shunt in one of the phases and compares the signal from this with phase voltage. The resultant lagging or leading dictates weather the set is generating or motoring.
The solution is to put by-pass contactors around the VSD's but this is not curing the problem.
Anyone any ideas?
Al