Equalizing Ground Fault
Power generation equipment control. topic
Posted by Shaheed on 2 July, 2012 - 6:46 am
How can we equalize the ground fault in ground fault current with open delta voltage?

A generator is protected by a ground fault CT of 200/5 set to 2.5A secondary. When synchronized with grid the NGR switched off and the only protection of ground fault depends on open delta PT 11KV/110V. Somebody can guide how much secondary voltage of open delta would be equal to 2.5A secondary fault current of CT?

Regards
Shaheed


Posted by Phil Corso on 2 July, 2012 - 11:44 am
Shaheed... PTs having their secondaries open-delta (connected) usually have their primary-windings connected phase-to-phase.

Thus, they will not respond to earth-faults!

Regards, Phil Corso


Posted by Phle Corso on 2 July, 2012 - 8:10 pm
Shaheed... also see:

http://www.control.com/thread/1026237476

Regards, Phil Corso

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
U: There's a U -- a Unicorn!
Run right up and rub its horn.
Look at all those points you're losing!
UMBER HULKS are so confusing.
-- The Roguelet's ABC
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive