Posted by jake on 4 July, 2012 - 6:41 am
I am working on a large network and was wondering the proper method in how to terminate the shield cable of an rs 485 cable. It will be used between a master and multiple slaves. I was guessing to terminate the shield on the master side but then what to do between slaves? I am not sure yet If I will be terminating on all of the slaves as well, or do I twist the shields of the two daisy chained cables together and tape them back? Honeywell network


1 out of 1 members thought this post was helpful...
Posted by David on 4 July, 2012 - 1:58 pm
From National's AN-1057 note on RS-485
https://www.national.com/an/AN/AN-1057.pdf

Generally, a shield connects to a solid ground (normally, the metal frame around the system or subsystem) with a low impedance at one end and a series RC network at the other. This arrangement prevents the flow of DC ground-loop currents in the shield.

Me - I ground the shield at the master and tie the shields together at each slave and float them.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Yes, but every time I try to see things your way, I get a headache.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive