Orifice type of differential pressure flow transmitter
PLCs and related questions. topic
Posted by Rahul on 5 July, 2012 - 12:11 pm
An orifice type flow transmitter having linear confirmity, so how to obtain actual flow? What is calculation to obtain square root extraction at plc end and what will be significance of K factor.
orifice plate 2500mmh2o at 8001kg/hr
transmitter cal. 0-2500mmh2o
k factor 1.3172


Posted by Carl Ellis on 8 July, 2012 - 9:04 am
See the 2nd post at this thread for an example of a DP square root for 1200mm DP/time unit.

http://tinyurl.com/7qbn9e7

There's one typo: 15% should be 16%


Posted by Rahul on 11 July, 2012 - 12:18 am
Thanks for the reply and can you tell how to consider the K Factor.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.