Raised stator winding temperature on GT MARK-II indicator was observed. 3 wire copper-10 RTDs installed on stator and cooling air path.
All RTDs have two separate positive and negative and a common compensation cable. But when we measured RTD temperature from JB5 it was less then what was being displayed e.g.
We replaced positive and negative cable of RTD-4 from JB to MARK-II control MARK-II indicator started displaying 100DegC.
Now my question is why all RTDs which are in error showing positive shift of temperature only??? why not negative?? all cables are equally old and they are a part of common jigg. I am only confused due to this positive increment of temperature and same is the case with our other GT. Thanks in anticipation.
Regards,
Adeel Imtiaz
All RTDs have two separate positive and negative and a common compensation cable. But when we measured RTD temperature from JB5 it was less then what was being displayed e.g.
JB(RTD Disconnected) MARK-II TI
RTD-1 103degC 100degC
RTD-2 103degC 115degC
RTD-3 101deGc 103degC
RTD-4 104DegC 118DegC
and so on
We replaced positive and negative cable of RTD-4 from JB to MARK-II control MARK-II indicator started displaying 100DegC.
Now my question is why all RTDs which are in error showing positive shift of temperature only??? why not negative?? all cables are equally old and they are a part of common jigg. I am only confused due to this positive increment of temperature and same is the case with our other GT. Thanks in anticipation.
Regards,
Adeel Imtiaz
![]() ![]() |
calibrate your GT temp:indicator as per copper-10 vs temp: standards graph.
![]() ![]() |
How are you measuring the RTD temp. at the JB? What are you using in your MKII panel to display your Stator winding temps?
![]() ![]() |
Many Mk-II-equipped units used interconnecting cables with pinned-and-socketed connectors on one or both cable ends. These are subject to corrosion if they were not properly tightened during original construction--and many weren't. Also many cable vaults/pits have been found to be filled with water and/or lube oil and the vapors are drawn into properly air conditioned compartments and can also contribute to corrosion.
You didn't indicate the results of checking the resistances of the individual conductors. You will likely find, after consulting an RTD table, that temperature indications increase with increasing resistance and so if there is increased resistance from conductors and/or corroded pins & sockets the indicated temperature will be abnormally high.
You didn't indicate the results of checking the resistances of the individual conductors. You will likely find, after consulting an RTD table, that temperature indications increase with increasing resistance and so if there is increased resistance from conductors and/or corroded pins & sockets the indicated temperature will be abnormally high.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.
Fortune
"I was gratified to be able to answer promptly, and I did. I said I
didn't know."
-- Mark Twain







on 15 July, 2012 - 5:55 am
on 15 July, 2012 - 9:41 pm