from the Forum department...
RTD connection to analogue input card
Sensor technologies. topic
Posted by Barker3k on 18 July, 2012 - 7:47 am
Can someone advise me whether there is anything which can be used to convert the 3 wired signal from an rtd into a 2 wire input into a foxboro I/A analogue input card?
The foxboro system was purchased before a started and there wasn't a dedicated rtd card purchased. Just wondering whether I can get round this little mess.
Hope someone can help.
Posted by David on 18 July, 2012 - 10:34 am
Can I assume that a 2 wire analog input is a conventional 4-20mA analog input?
If so, you need to look for a 2 wire, loop powered "temperature transmitter" that handles an RTD input (some models are thermocouple only input). There are hundreds of manufacturers of such.
The transmitter will need its output range configured; where 4mA represents some low temperature and 20mA represents some high temperature, for instance, 0-200°C.
Some are configured at the factory. Some use a manufacturer's software and cable (which might cost more than the transmitter). High end transmitter models can be field configured with HART, which requires an expensive handheld communicator.
Most people who have a DCS also have a handheld HART communicator, but check with your instrument guy first. If not, get a transmitter that is factory configured for your range or have your local vendor range it for you.
Posted by bob peterson on 18 July, 2012 - 12:04 pm
An RTD is just a variable resistor. Ohm's law would solve your problem.
Bob
Real Users hate Real Programmers.