Posted by engineer on 18 July, 2012 - 12:19 pm
hi all,

need a rough relationship between a given kva feeding transformer and the maximum hp motor that would run good with dol connection


Posted by engineer on 19 July, 2012 - 2:25 pm
the summary (the one liner) "maximum hp motor for dol starting with given kva transformer" as its written, is a mistake.

kindly read it as "maximum hp dol connected motor with a given kva transformer"


Posted by William Hinton on 21 July, 2012 - 11:04 am
As you did not specify a transformer type, voltage class, kVA or hp, I will give you an example:

Typically you would use a 2,000 kVA power transformer to start and run a 1,500 hp motor across-the-line (dol)

This is for a 4,160 volt 3-phase 4-wire feed to the drive motor in an air compressor.

I hope this helps,
William Hinton


Posted by Phil Corso on 21 July, 2012 - 5:03 pm
William... I would be very interested in the motor's kVA/Hp ratio?

Regards, Phil


Posted by Phil Corso on 22 July, 2012 - 5:14 pm
William... I meant NEMA Locked-Rotor Code.

Phil


Posted by engineer on 24 July, 2012 - 12:22 pm
dear phil corso and william hinton,
thanks

the basic idea i started out with is, the maximum hp (dol) starting depends on the capacity of the power system, its ability to provide current and tolerate voltage drop.

if i increase the kva of the transformer, i can increase the hp of the motor?
i was looking for a rough estimate, how much hp change for some kva change(general, a rough graph), if its there.

and please correct me if i am wrong somewhere :)


Posted by Phil Corso on 24 July, 2012 - 3:37 pm
Engineer... since the V-Drop experienced by the motor is proportional to the load carried by the xfmr, there is an easier way!

If the Transformer Capacity (kVAc) and Percent Impedance Voltage (Zt) are known, as well as the Starting kVA, then use the following solution:

1) Calculate the short-circuit duty at the transformer secondary:

kVAsc = (kVAc)/(%Zt/100)

2) Calculate the Starting kVA of the motor.

kVAsm = (kVA/Hp)x Hp

3) Calculate the V-Drop to Motor.

V-Drop, % = 100x(kVAsm/kVAsc)

4) Example:
Xfmr = 1,500kVA,Z = 5.0%;
Mtr = 200Hp, Start kVA/Hp = 6.0

a) kVAsc = 1,500/(5.0/100) = 30,000kVA

b) kVAsm = 6.0 x 300 = 1,800kVA

c) V-D,% = 100 x 1,800/30,000 = 6.0%

The above should be adequate for the solution to your problem.

Regards,
Phil


Posted by Phil Corso on 24 July, 2012 - 4:49 pm
Engineer... I committed three (3) 'OOPs' (the most feared word in an operating-room):

OOPs 1) I neglected to mention my solution was loosely based on a transformer's Regulation Factor. That is Reg (%) = 100 x (VNL-VFL)/VFL.

OOPs 2) Motor Starting-current is assumed to be inductive, thus lagging.

OOPs 3) The final V-Drop, then equals, VDm'= V-Drop x Zt. So for the example, VDm' = 0.05 x 5% = 0.3%.

Phil Corso

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
When Marriage is Outlawed,
Only Outlaws will have Inlaws.
Advertise here
advertisements
Time to incorporate data handling, web HMI and motion in one system!
Servo, steppers, analog, digital & web HMI - Fully Integrated!
Servo, stepping motor control, analog & web HMI in one system!
Control.com is the largest Automation community on the web. Learn how to advertise here now...
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive