GT v ST loads
Power generation equipment control. topic
Posted by Andrew on 19 July, 2012 - 6:50 am
Is there a rule of thumb for estimating (guestimating) the load of the ST & GT when the Generated load is known?

Example, on a single shaft where there is one generator, we can only see the generated load.

How would you split the Generated load between the GT and ST?

I understand that at varying loads the "split" will migrate due to fluctuation in back pressure, opening of blow downs, etc.
But I was hoping that somewhere at a quick glance there was a common train of thought that said the split would be 'x' %GT and 'x' %ST.

Anyone??


2 out of 2 members thought this post was helpful...
Posted by MIKEVI on 19 July, 2012 - 10:38 am
Andrew,

not sure if this answers your question but I will try. As you say it will depend on the efficiency and heat rate of your gas turbine, steam turbine and boiler. But my experience is that you can expect to get 40-60% of the gas turbine load from the steam turbine on most newer gas turbines with systems that have logic to maximize heat efficiency from the GTG. For instance with gas turbine load at 50MW expect 25-30MW from the STG.


2 out of 2 members thought this post was helpful...
Posted by otised on 19 July, 2012 - 11:16 am
The general rule of thumb is the gas turbine(s) will provide 2/3 of the load and the steam turbine will provide 1/3 of the load. These numbers are approximate, and will vary when the load is changing. This split is true for single shaft and multi shaft combined cycle applications, where all the steam produced goes to the steam turbine and there are no extractions (cogeneration applications).


Posted by Andrew on 24 July, 2012 - 12:15 pm
Thank you very much. I thought I would share my findings after much data crunching, and I must say the rule of thumb of 40/60 split or 2/3 over 1/3 is as close as one can get. The grater the load is, the greater the split. Using linier data the best I can pin it down to is that the ST will be delivering approximately 50 & 54% of the GT (depending on load).

@ High load GT/ST Split of: 68 % & 32 %
Ex: Generated load 370 = GT @68%=252MW & ST @32%=118 MW =(46% of GT load)

@ Low load 63% & 37 %
Ex: Generated load 230 = GT @63%=145MW & ST @37%=85 = (58% of GT load)


Posted by CSA on 25 July, 2012 - 3:04 pm
Thanks for the feedback!



1 out of 1 members thought this post was helpful...
Posted by MIKEVI on 25 July, 2012 - 8:47 pm
Andrew, thanks for the feedback!!

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
"I was playing poker the other night ... with Tarot cards. I got a full
house and four people died."
-- Steven Wright
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive