We all know that trip protection provided for low vacuum in steam turbine. but my question is What happens if we maintain high high vacuum in the condenser?
![]() ![]() |
Good if you can. The questions is how you are going to do it? Vacuum pressure is determined by saturation temperature. The lowest saturation temperature you can maintain is about 2-3 Degree Celsius above inlet temperature of the condenser circulating water.
Theoretically there is one way you can do it. Just eject out certain amount of steam from your hotwell to bring down saturation pressure, thus to increase vacuum pressure. The only problem is you may find that your demin plant may not big enough to provide makeup water for your boiler.
Theoretically there is one way you can do it. Just eject out certain amount of steam from your hotwell to bring down saturation pressure, thus to increase vacuum pressure. The only problem is you may find that your demin plant may not big enough to provide makeup water for your boiler.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.